[RE-wrenches] Rapid Shutdown for Off-grid systems

Brian Mehalic brian at solarenergy.org
Tue Feb 1 14:20:51 EST 2022


A switch, outside of the building, opening the PV circuit to the power electronics, and functioning as the pv system disco and the rapid shutdown initiation device, should be all that is required. 

Brian

> On Feb 1, 2022, at 11:43 AM, Christopher Warfel <cwarfel at entech-engineering.com> wrote:
> 
> 
> That was my understanding too, but the language Jay has from 2017 (and I confirmed in 2020) reads different.  I was positive ground mounted arrays did not need to comply with RSS. The bogus argument made by the businesses influencing the CMP, and by a few mercenaries supposedly representing firefighter concerns was explicitly for roof mounted systems going through its history.  Chris
> 
>> On 2/1/2022 1:11 PM, Ray wrote:
>>  Ground mounts do NOT require RSS.  We hashed this out years ago on the Wrenches list, when NEC 2017 came out.
>> 
>> See Figure 690.1(B) Note (2): " The PV system disconnect in these diagrams separates the PV system from all other systems".
>> 
>> Thus, the PV disconnect is defined as the transition point from the PV system to all other systems, like battery or inverter systems. The installer/ designer decides where to put that disconnect.  I usually put it on the wall before it goes into the building, and I have never had an inspector question that. 
>> 
>> Thanks,
>> 
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 2/1/22 10:06 AM, William Miller wrote:
>>> Jay:
>>>  
>>> Here is the text from 2017:
>>>  
>>> 690.12 Rapid Shutdown of PV Systems on Buildings. PV
>>> system circuits installed on or in buildings shall include a rapid
>>> shutdown function to reduce shock hazard for emergency
>>> responders in accordance with 690.12(A) through (D).
>>>  
>>> Exception: Ground mounted PV system circuits that enter buildings, of
>>> which the sole purpose is to house PV system equipment, shall not be
>>> required to comply with 690.12.
>>>  
>>> The wording is interesting.  The requirement is directed at “PV system circuits…”, not PV arrays.  The passage does not specify where the PV feeding those circuits is located, it just addresses where the circuits are, specifically “in or on a building.”
>>>  
>>> The only circuits that are exempt are those feeding a building that serves only one purpose, to house PV equipment.  For circuits that enter building with other uses—homes, garages, barns, workshops, etc.-- it would seem there is a requirement to have rapid shutdown systems (RSS).
>>>  
>>> Reading through the rest of the section, I don’t see any language that gets us out of the requirement to reduce voltages to less than 80 volts within 30 seconds inside the array boundary, as in module level shutdown, regardless of roof-top or ground-mount.  Although the 2020 code includes some differing language, I don’t see it as exempting ground mount systems.
>>>  
>>> The moral of the story is this:  For ground-mounts:  either install RSS or put your equipment (inverters, charge controllers, batteries, BOS) in a separate building housing only that equipment.
>>>  
>>> I don’t necessarily like the requirement, but I think it exists.  Jay, or anyone, please, please tell me I am reading this incorrectly. 
>>>  
>>> By the way, regarding battery circuits, here is a quote from a post by Bill Brooks on March 16, 2016:
>>>  
>>> In the 2017 NEC, we were very careful to carve out all batteries and loads,
>>> that were previously part of PV systems, and place them in their own
>>> articles.
>>>  
>>> I have not read through the battery sections of the code to verify this, I am taking Bill at his word.
>>>  
>>> William Miller
>>>  
>>> Miller Solar
>>> 17395 Oak Road, Atascadero, CA 93422
>>> 805-438-5600
>>> www.millersolar.com
>>> CA Lic. 773985
>>>  
>>>  
>>> From: Jay [mailto:jay.peltz at gmail.com] 
>>> Sent: Tuesday, February 1, 2022 6:07 AM
>>> To: william at millersolar.com; RE-wrenches
>>> Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>>>  
>>> 2017 code has a specific exception/clarification for ground mount solar that it does not need RS. 
>>> It’s in the first line after 690.12
>>>  
>>> Jay
>>> 
>>> 
>>> On Feb 1, 2022, at 12:13 AM, William Miller <william at millersolar.com> wrote:
>>> 
>>> 
>>> Jerry:
>>>  
>>> Yes it is required.  Rapid Shutdown:  NEC 690.12.  All buildings except dedicated solar buildings.  Read it and weep.
>>>  
>>> William
>>>  
>>> Miller Solar
>>> 17395 Oak Road, Atascadero, CA 93422
>>> 805-438-5600
>>> www.millersolar.com
>>> CA Lic. 773985
>>>  
>>>  
>>> From: Jerry Shafer [mailto:jerrysgarage01 at gmail.com] 
>>> Sent: Monday, January 31, 2022 7:21 PM
>>> To: William Miller; RE-wrenches
>>> Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>>>  
>>> William
>>> Are you sure RSD is required on a non habitable building, historically its not required. Now that being said we use fire raptor with the best results, yes it takes an extra conduite and might require a button and power supply depending on inverter application.
>>> Jerry
>>>  
>>> On Mon, Jan 31, 2022, 9:57 AM William Miller <william at millersolar.com> wrote:
>>> Friends:
>>>  
>>> It is quite rare for us to install off-grid systems on roof-tops.  We have one coming up with about 20kW on a large barn roof.  This will be our first off-grid with a module-level rapid shutdown requirement.  I see no exemptions from RSS for off-grid systems in the code.  I have looked at the options and this is what I have found:
>>>  
>>> 1.   Fire Raptor
>>> 
>>> 2.   Tigo TS4-F
>>> 
>>> 3.   AC coupling with micro-inverters or optimizers
>>> 
>>>  
>>> No one of these approaches seems ideal.  The fire raptor requires extra wiring for control leads.  The Tigo requires a wireless control system which worries me about reliability.  With AC Coupling systems floating the proposed AGM batteries may be awkward.  Furthermore, with AC coupled systems one cannot charge batteries unless the mini-grid is operational, a big problem.
>>>  
>>> Have any of you implemented module-level RSS on a battery-based inverter system?  I looked in the archives and found no threads that apply.  Thank in advance.
>>>  
>>> William Miller
>>>  
>>> 
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> -- 
>                                          Christopher Warfel
>                      ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
>                                                             401-466-8978
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/e4772487/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/e4772487/attachment.jpg>


More information about the RE-Wrenches mailing list