That was my understanding too, but the language Jay has from 2017 (and I 
confirmed in 2020) reads different.  I was positive ground mounted 
arrays did not need to comply with RSS. The bogus argument made by the 
businesses influencing the CMP, and by a few mercenaries supposedly 
representing firefighter concerns was explicitly for roof mounted 
systems going through its history.  Chris

On 2/1/2022 1:11 PM, Ray wrote:
>
>  Ground mounts do NOT require RSS.  We hashed this out years ago on 
> the Wrenches list, when NEC 2017 came out.
>
> See Figure 690.1(B) Note (2): /" The PV system disconnect in these 
> diagrams separates the PV system from all other systems"./
>
> Thus, the PV disconnect is defined as the transition point from the PV 
> system to all other systems, like battery or inverter systems. The 
> installer/ designer decides where to put that disconnect.  I usually 
> put it on the wall before it goes into the building, and I have never 
> had an inspector question that.
>
> Thanks,
>
> Ray Walters
> Remote Solar
> 303 505-8760
> On 2/1/22 10:06 AM, William Miller wrote:
>>
>> Jay:
>>
>> Here is the text from 2017:
>>
>> /690.12 Rapid Shutdown of PV Systems on Buildings. PV/
>>
>> /system circuits installed on or in buildings shall include a rapid/
>>
>> /shutdown function to reduce shock hazard for emergency/
>>
>> /responders in accordance with 690.12(A) through (D)./
>>
>> //
>>
>> /Exception: Ground mounted PV system circuits that enter buildings, of/
>>
>> /which the sole purpose is to house PV system equipment, shall not be/
>>
>> /required to comply with 690.12./
>>
>> The wording is interesting.  The requirement is directed at “PV 
>> system circuits…”, not PV arrays.  The passage does not specify where 
>> the PV feeding those circuits is located, it just addresses where the 
>> circuits are, specifically “in or on a building.”
>>
>> The only circuits that are exempt are those feeding a building that 
>> serves only one purpose, to house PV equipment.  For circuits that 
>> enter building with other uses—homes, garages, barns, workshops, 
>> etc.-- it would seem there is a requirement to have rapid shutdown 
>> systems (RSS).
>>
>> Reading through the rest of the section, I don’t see any language 
>> that gets us out of the requirement to reduce voltages to less than 
>> 80 volts within 30 seconds inside the array boundary, as in module 
>> level shutdown, regardless of roof-top or ground-mount.  Although the 
>> 2020 code includes some differing language, I don’t see it as 
>> exempting ground mount systems.
>>
>> The moral of the story is this:  For ground-mounts:  either install 
>> RSS or put your equipment (inverters, charge controllers, batteries, 
>> BOS) in a separate building housing only that equipment.
>>
>> I don’t necessarily like the requirement, but I think it exists.  
>> Jay, or anyone, please, please tell me I am reading this incorrectly.
>>
>> By the way, regarding battery circuits, here is a quote from a post 
>> by Bill Brooks on March 16, 2016:
>>
>> /In the 2017 NEC, we were very careful to carve out all batteries and 
>> loads,/
>>
>> /that were previously part of PV systems, and place them in their own/
>>
>> /articles./
>>
>> I have not read through the battery sections of the code to verify 
>> this, I am taking Bill at his word.
>>
>> William Miller
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com <http://www.millersolar.com/>
>>
>> CA Lic. 773985
>>
>> *From:*Jay [mailto:jay.peltz at gmail.com]
>> *Sent:* Tuesday, February 1, 2022 6:07 AM
>> *To:* william at millersolar.com; RE-wrenches
>> *Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>>
>> 2017 code has a specific exception/clarification for ground mount 
>> solar that it does not need RS.
>>
>> It’s in the first line after 690.12
>>
>> Jay
>>
>>
>>
>> On Feb 1, 2022, at 12:13 AM, William Miller <william at millersolar.com> 
>> wrote:
>>
>>     
>>
>>     Jerry:
>>
>>     Yes it is required.  Rapid Shutdown:  NEC 690.12.  All buildings
>>     except dedicated solar buildings.  Read it and weep.
>>
>>     William
>>
>>     Miller Solar
>>
>>     17395 Oak Road, Atascadero, CA 93422
>>
>>     805-438-5600
>>
>>     www.millersolar.com <http://www.millersolar.com/>
>>
>>     CA Lic. 773985
>>
>>     *From:*Jerry Shafer [mailto:jerrysgarage01 at gmail.com]
>>     *Sent:* Monday, January 31, 2022 7:21 PM
>>     *To:* William Miller; RE-wrenches
>>     *Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>>
>>     William
>>
>>     Are you sure RSD is required on a non habitable building,
>>     historically its not required. Now that being said we use fire
>>     raptor with the best results, yes it takes an extra conduite and
>>     might require a button and power supply depending on inverter
>>     application.
>>
>>     Jerry
>>
>>     On Mon, Jan 31, 2022, 9:57 AM William Miller
>>     <william at millersolar.com> wrote:
>>
>>         Friends:
>>
>>         It is quite rare for us to install off-grid systems on
>>         roof-tops.  We have one coming up with about 20kW on a large
>>         barn roof.  This will be our first off-grid with a
>>         module-level rapid shutdown requirement.  I see no exemptions
>>         from RSS for off-grid systems in the code.  I have looked at
>>         the options and this is what I have found:
>>
>>         1.Fire Raptor
>>
>>         2.Tigo TS4-F
>>
>>         3.AC coupling with micro-inverters or optimizers
>>
>>         No one of these approaches seems ideal.  The fire raptor
>>         requires extra wiring for control leads.  The Tigo requires a
>>         wireless control system which worries me about reliability. 
>>         With AC Coupling systems floating the proposed AGM batteries
>>         may be awkward.  Furthermore, with AC coupled systems one
>>         cannot charge batteries unless the mini-grid is operational,
>>         a big problem.
>>
>>         Have any of you implemented module-level RSS on a
>>         battery-based inverter system?  I looked in the archives and
>>         found no threads that apply. Thank in advance.
>>
>>         William Miller
>>
>>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/ebf7b14b/attachment.htm>