Hi, If I put a disconnect switch within one foot of the ground mounted 
array, I am pretty sure this would comply with RSS requirements?  Chris

On 2/1/2022 12:06 PM, William Miller wrote:
>
> Jay:
>
> Here is the text from 2017:
>
> /690.12 Rapid Shutdown of PV Systems on Buildings. PV/
>
> /system circuits installed on or in buildings shall include a rapid/
>
> /shutdown function to reduce shock hazard for emergency/
>
> /responders in accordance with 690.12(A) through (D)./
>
> //
>
> /Exception: Ground mounted PV system circuits that enter buildings, of/
>
> /which the sole purpose is to house PV system equipment, shall not be/
>
> /required to comply with 690.12./
>
> The wording is interesting.  The requirement is directed at “PV system 
> circuits…”, not PV arrays.  The passage does not specify where the PV 
> feeding those circuits is located, it just addresses where the 
> circuits are, specifically “in or on a building.”
>
> The only circuits that are exempt are those feeding a building that 
> serves only one purpose, to house PV equipment.  For circuits that 
> enter building with other uses—homes, garages, barns, workshops, 
> etc.-- it would seem there is a requirement to have rapid shutdown 
> systems (RSS).
>
> Reading through the rest of the section, I don’t see any language that 
> gets us out of the requirement to reduce voltages to less than 80 
> volts within 30 seconds inside the array boundary, as in module level 
> shutdown, regardless of roof-top or ground-mount.  Although the 2020 
> code includes some differing language, I don’t see it as exempting 
> ground mount systems.
>
> The moral of the story is this:  For ground-mounts:  either install 
> RSS or put your equipment (inverters, charge controllers, batteries, 
> BOS) in a separate building housing only that equipment.
>
> I don’t necessarily like the requirement, but I think it exists.  Jay, 
> or anyone, please, please tell me I am reading this incorrectly.
>
> By the way, regarding battery circuits, here is a quote from a post by 
> Bill Brooks on March 16, 2016:
>
> /In the 2017 NEC, we were very careful to carve out all batteries and 
> loads,/
>
> /that were previously part of PV systems, and place them in their own/
>
> /articles./
>
> I have not read through the battery sections of the code to verify 
> this, I am taking Bill at his word.
>
> William Miller
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com <http://www.millersolar.com/>
>
> CA Lic. 773985
>
> *From:*Jay [mailto:jay.peltz at gmail.com]
> *Sent:* Tuesday, February 1, 2022 6:07 AM
> *To:* william at millersolar.com; RE-wrenches
> *Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>
> 2017 code has a specific exception/clarification for ground mount 
> solar that it does not need RS.
>
> It’s in the first line after 690.12
>
> Jay
>
>
>
> On Feb 1, 2022, at 12:13 AM, William Miller <william at millersolar.com> 
> wrote:
>
>     
>
>     Jerry:
>
>     Yes it is required.  Rapid Shutdown:  NEC 690.12.  All buildings
>     except dedicated solar buildings.  Read it and weep.
>
>     William
>
>     Miller Solar
>
>     17395 Oak Road, Atascadero, CA 93422
>
>     805-438-5600
>
>     www.millersolar.com <http://www.millersolar.com/>
>
>     CA Lic. 773985
>
>     *From:*Jerry Shafer [mailto:jerrysgarage01 at gmail.com]
>     *Sent:* Monday, January 31, 2022 7:21 PM
>     *To:* William Miller; RE-wrenches
>     *Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>
>     William
>
>     Are you sure RSD is required on a non habitable building,
>     historically its not required. Now that being said we use fire
>     raptor with the best results, yes it takes an extra conduite and
>     might require a button and power supply depending on inverter
>     application.
>
>     Jerry
>
>     On Mon, Jan 31, 2022, 9:57 AM William Miller
>     <william at millersolar.com> wrote:
>
>         Friends:
>
>         It is quite rare for us to install off-grid systems on
>         roof-tops.  We have one coming up with about 20kW on a large
>         barn roof.  This will be our first off-grid with a
>         module-level rapid shutdown requirement.  I see no exemptions
>         from RSS for off-grid systems in the code.  I have looked at
>         the options and this is what I have found:
>
>         1.Fire Raptor
>
>         2.Tigo TS4-F
>
>         3.AC coupling with micro-inverters or optimizers
>
>         No one of these approaches seems ideal.  The fire raptor
>         requires extra wiring for control leads.  The Tigo requires a
>         wireless control system which worries me about reliability. 
>         With AC Coupling systems floating the proposed AGM batteries
>         may be awkward.  Furthermore, with AC coupled systems one
>         cannot charge batteries unless the mini-grid is operational, a
>         big problem.
>
>         Have any of you implemented module-level RSS on a
>         battery-based inverter system?  I looked in the archives and
>         found no threads that apply.  Thank in advance.
>
>         William Miller
>
>         Miller Solar
>
>         17395 Oak Road, Atascadero, CA 93422
>
>         805-438-5600
>
>         www.millersolar.com <http://www.millersolar.com/>
>
>         CA Lic. 773985
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         Pay optional member dues here: http://re-wrenches.org
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         There are two list archives for searching. When one doesn't
>         work, try the other:
>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>         List rules & etiquette:
>         http://www.re-wrenches.org/etiquette.htm
>
>         Check out or update participant bios:
>         http://www.members.re-wrenches.org
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     Pay optional member dues here: http://re-wrenches.org
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     There are two list archives for searching. When one doesn't work,
>     try the other:
>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     http://www.re-wrenches.org/etiquette.htm
>
>     Check out or update participant bios:
>     http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/4db278bf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/4db278bf/attachment.jpg>


More information about the RE-Wrenches mailing list