Hi August;
I'm glad you brought this up. When I first saw only the hots being
brought to the Critical Load Panel, I thought it was wrong too, but then
I recalled that this is similar to a switch leg. Does 300.3 forbid
switch legs too? the exception in 404.2(A) allows switch legs, but
does it apply here? I don't have a definitive answer in regard to
300.3, other than to note it has numerous exceptions. 300.3(B)(4) may
also apply, and further, over current device enclosures and J boxes are
not specifically mentioned either.
To be clear, I am not the originator of this idea; I just copied this
method from Reliance and Generac's wiring of their UL listed circuit
transfer switches. I have used it since 2003, and never had an AHJ have
an objection. I've discussed it with AHJs and electricians that
specialize in generators, and this is common when retrofitting a backup
generator.
Also in response to the person that posted about having trouble with the
neutrals: we have no neutrals at all in the CLP, if done this way. All
neutrals land on the main neutral buss in the main panel. The CLP only
has hots to the breakers, and the "neutral" bar in the CLP is used only
as the equipment ground for the enclosure by adding the green bonding
screw.
To be clear, I would not use this method on new construction where the
branch circuits could be brought straight to the CLP. This is for
*retrofit only*. I also would not do this if the CLP and main panel
were connected with a nipple longer than 24". Further, I over size the
nipple and use PVC to reduce any possible inductive heating issues. For
very short nipples, I have to use RMC, but I would never use EMT.
This method helps keep the space requirements down to comply with
312.8(2), and keeps the wiring cleaner, fewer splices, and less over all
disturbance to existing wiring in the sometimes aging and crowded main
load center.
The trade off is possible inductive heating of a short nipple caused
only by lower current 120 vac circuits (the 240 vac hots cancel each
other's inductance).
Again, I'm not the AHJ, and I'm not the originator of this method. I'm
just doing my best to describe a method used in the backup generator
world that I've found helpful.
The NEC and our work essentially is a compromise of numerous competing
safety concerns. The code describes many wiring methods; its up to us
to optimize each situation for overall safety.
Here's a screen shot from the Reliance manual:
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 9/9/2016 12:45 PM, August Goers wrote:
>
> Ray,
>
> I’m intrigued by this. We’ve always gone off NEC 300.3(B):
>
> (B) Conductors of the Same Circuit. All conductors of
>
> the same circuit and, where used, the grounded conductor
>
> and all equipment grounding conductors and bonding conductors
>
> shall be contained within the same raceway, auxiliary
>
> gutter, cable tray, cablebus assembly, trench, cable, or
>
> cord, unless otherwise permitted in accordance with
>
> 300.3(B)(1) through (B)(4).
>
> I interpret this to mean that we need to run neutrals along with any
> branch circuits we are moving over.
>
> Best,
>
> August
>
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Ray
> Walters
>
> Sent: Thursday, September 08, 2016 5:44 PM
>
> To: RE-wrenches
>
> Subject: Re: [RE-wrenches] Splices in service panel
>
> Hi Chris;
>
> Its the same as a switch leg for a light. The neutral stays at the
> light, only the hot is run down to the switch and back.
>
> Also, with some critical load panel set ups available (ie Generac),
> there is no provision to even run the neutrals to the new CLP.
>
> This is cleaner and involves much less splicing. Fewer connections is
> usually better in my book.
>
> R.Ray Walters
>
> CTO, Solarray, Inc
>
> Nabcep Certified PV Installer,
>
> Licensed Master Electrician
>
> Solar Design Engineer
>
> 303 505-8760
>
> On 9/8/2016 6:22 PM, Chris Mason wrote:
>
> I disagree with the response that you do not need to move the
> neutrals. You should never have the load's phase wiring in one panel
> and the neutral in another.
>
> Chris Mason
>
> NABCEP Certified Solar PV Installer™
>
> Solar Design Engineer
>
> Generac Generators Industrial technician
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160910/724ea5b6/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: khlejeopibpcegmm.jpg
Type: image/jpeg
Size: 129951 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160910/724ea5b6/attachment-0004.jpg>
More information about the RE-wrenches
mailing list