Ray,
I’m intrigued by this. We’ve always gone off NEC 300.3(B):
(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with
300.3(B)(1) through (B)(4).
I interpret this to mean that we need to run neutrals along with any branch
circuits we are moving over.
Best,
August
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Ray Walters
Sent: Thursday, September 08, 2016 5:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Splices in service panel
Hi Chris;
Its the same as a switch leg for a light. The neutral stays at the light,
only the hot is run down to the switch and back.
Also, with some critical load panel set ups available (ie Generac), there
is no provision to even run the neutrals to the new CLP.
This is cleaner and involves much less splicing. Fewer connections is
usually better in my book.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 9/8/2016 6:22 PM, Chris Mason wrote:
I disagree with the response that you do not need to move the neutrals. You
should never have the load's phase wiring in one panel and the neutral in
another.
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician