Kristopher Schmid solman at legacysolar.com
Mon Mar 21 14:58:04 PDT 2016


I just did a class exercise using the upcoming sw290 for sizing conductors
and OCPD and the calculation was such that a 20 amp fuse was needed
(rounding up from Isc x 1.56).  I hope that the maximum reverse current on
the spec sheet is also the maximum series fuse rating.

Kris
On Mar 18, 2016 8:56 PM, "jay" <jay.peltz at gmail.com> wrote:

> HI All,
>
> I was looking at the SW cut sheet.
> It doesn’t mention series fuse rating.
>
> It does mention “maximum reverse current”
> Is this the same thing?
>
> Or where would I find the series fuse rating.
>
> thanks
>