[RE-wrenches] SW series fuse rating

Rebekah Hren rebekah.hren at gmail.com
Mon Mar 21 15:32:07 PDT 2016


Reverse current and max series fuse are not always the same, check out this
Solar Frontier manual, pg 3:

http://www.solar-frontier.com/eng/cs/groups/co_en_product/documents/document/mdaw/mdey/~edisp/c012760.pdf


Rebekah Hren

On Mon, Mar 21, 2016 at 3:58 PM, Kristopher Schmid <solman at legacysolar.com>
wrote:

> I just did a class exercise using the upcoming sw290 for sizing conductors
> and OCPD and the calculation was such that a 20 amp fuse was needed
> (rounding up from Isc x 1.56).  I hope that the maximum reverse current on
> the spec sheet is also the maximum series fuse rating.
>
> Kris
> On Mar 18, 2016 8:56 PM, "jay" <jay.peltz at gmail.com> wrote:
>
>> HI All,
>>
>> I was looking at the SW cut sheet.
>> It doesn’t mention series fuse rating.
>>
>> It does mention “maximum reverse current”
>> Is this the same thing?
>>
>> Or where would I find the series fuse rating.
>>
>> thanks
>>
>> jay
>>
>> peltz power
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160321/3133f651/attachment-0002.html>


More information about the RE-wrenches mailing list