<p dir="ltr">I just did a class exercise using the upcoming sw290 for sizing conductors and OCPD and the calculation was such that a 20 amp fuse was needed (rounding up from Isc x 1.56).  I hope that the maximum reverse current on the spec sheet is also the maximum series fuse rating.</p>
<p dir="ltr">Kris</p>
<div class="gmail_quote">On Mar 18, 2016 8:56 PM, "jay" <<a href="mailto:jay.peltz@gmail.com">jay.peltz@gmail.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">HI All,<br>
<br>
I was looking at the SW cut sheet.<br>
It doesn’t mention series fuse rating.<br>
<br>
It does mention “maximum reverse current”<br>
Is this the same thing?<br>
<br>
Or where would I find the series fuse rating.<br>
<br>
thanks<br>
<br>
jay<br>
<br>
peltz power<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>