[RE-wrenches] SW series fuse rating

Bill Hoffer sunengser at gmail.com
Fri Mar 18 22:22:53 PDT 2016


Jay
I believe that is the same.  I hate that they say it that way...very
confusing.  I think it comes from the way it is tested by UL.  They reverse
current  at 1.5 times the fuse rating to insure the fuse size is correct
(fuse plus safety factor).

Bill
On Mar 18, 2016 6:56 PM, "jay" <jay.peltz at gmail.com> wrote:

> HI All,
>
> I was looking at the SW cut sheet.
> It doesn’t mention series fuse rating.
>
> It does mention “maximum reverse current”
> Is this the same thing?
>
> Or where would I find the series fuse rating.
>
> thanks
>
> jay
>
> peltz power
>