At 02:35 PM 10/10/2009, you wrote:
>. How do we bond both ends of the conduit?

How about using a water pipe clamps on the EMT.  A bare copper, # 6 
or larger, should be able to be run outside the conduit, as it is a 
bond between sub arrays.  My reading is that, from the combiner box 
on,  an equipment grounding conductor would need to be inside the conduit.