At 02:35 PM 10/10/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">. How do we bond both ends of
the conduit?</blockquote><br>
<font color="#0000FF">How about using a water pipe clamps on the
EMT.  A bare copper, # 6 or larger, should be able to be run outside
the conduit, as it is a bond between sub arrays.  My reading is
that, from the combiner box on,  an equipment grounding conductor
would need to be inside the conduit.  <br><br>