[RE-wrenches] Rooftop wiring methods between multiple subarrays

Max Balchowsky max at seesolar.com
Mon Oct 12 17:44:13 PDT 2009


If your talking about conduit runs between arrays, we've always used minerallac clamps to attach to either the riser, or the frame, depending on the tilt angle and accessibility. The inspector has always accepted this as bonding between arrays.....

Max Balchowsky
SEE Systems

760-403-6810




________________________________
From: Drake Chamberlin <drake.chamberlin at redwoodalliance.org>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Sunday, October 11, 2009 7:38:28 AM
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

 At 02:35 PM 10/10/2009, you wrote:

. How do we bond both ends of
>the conduit?
How about using a water pipe clamps on the
EMT.  A bare copper, # 6 or larger, should be able to be run outside
the conduit, as it is a bond between sub arrays.  My reading is
that, from the combiner box on,  an equipment grounding conductor
would need to be inside the conduit.  