You may also want to look at the Victron products. They have a 1000 amp version called the Lynx distributor.
Peter Giroux
ASAE
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Bradley Bassett via RE-wrenches
Sent: Thursday, June 29, 2023 10:47 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Bradley Bassett <bbassett2 at gmail.com>
Subject: Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar
Note that MidNite now also makes 2000A and 500A versions of their BCB. With two Sol-Ark 15k you do need to use the 1000A version with 275A each inverter. I can also confirm that you do need to use both of the battery terminals in the Sol-Ark 15k for full power, or the Homegrid bus bars that Jason shows.
Brad Bassett
On Thu, Jun 29, 2023 at 6:57 AM Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:
Lloyd,
Homegrid makes a busbar to combine the two terminals in the Sol-Ark 15k so it can accept a single 4/0 cable and retain the full output capacity. Apparently, Homegrid is the only battery on the market with the output capacity to do this.
https://www.homegridenergy.com/stackd-series <https://mailtrack.io/trace/link/a0cf1afc125652c2027c1cbd7d5458266a2d118b?url=https%3A%2F%2Fwww.homegridenergy.com%2Fstackd-series&userId=1613865&signature=28245d1e93ba151a>
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
On Thu, Jun 29, 2023 at 9:43 AM Lloyd Hoffstatter via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:
Hi Maverick,
Per tech support, you need to buss battery output(s) to both input breakers to get the full 275 Amp output.
Best regards,
Lloyd
Lloyd Hoffstatter, M.S. Applied Solar Energy
NABCEP Inaugural Certified PV Installer Emeritus
Director, Sunstruck Consulting
Lloyd at SunstruckConsulting.com <mailto:Lloyd at SunstruckConsulting.com>
845-657-8132 (office)
914-844-3404 (mobile)
From: Mac Lewis via RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
Sent: Thursday, June 29, 2023 8:27 AM
To: RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
Cc: Mac Lewis <mailto:maclewis1 at gmail.com>
Subject: Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar
Hi Jason,
The Sol-Ark 15k has dual battery input terminals so they can be combined right inside. This could be a good option to consider.
Thanks
On Thu, Jun 29, 2023 at 6:17 AM Maverick Brown via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:
I recommend the Victron Lynx Power In or the Lynx Distributor.
Thank you,
Maverick
On Jun 29, 2023, at 6:55 AM, Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:
Hi all,
I'm doing my first installation with two 24 kWh Homegrid stacks. They will feed two Sol-Ark 15k. I'm seeking recommendations on busbars for connecting this up in the most elegant way possible.
Pictures speak 1,000 words, so if you have any I would appreciate it (off-list is fine).
Jason Szumlanski
Florida Solar Design Group
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230629/ceffe63b/attachment.htm>
More information about the RE-Wrenches
mailing list