[RE-wrenches] Parallel Homegrid Stack'd Busbar

Bradley Bassett bbassett2 at gmail.com
Thu Jun 29 10:46:46 EDT 2023


Note that MidNite now also makes 2000A and 500A versions of their BCB. With
two Sol-Ark 15k you do need to use the 1000A version with 275A each
inverter. I can also confirm that you do need to use both of the battery
terminals in the Sol-Ark 15k for full power, or the Homegrid bus bars that
Jason shows.

Brad Bassett


On Thu, Jun 29, 2023 at 6:57 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Lloyd,
>
> Homegrid makes a busbar to combine the two terminals in the Sol-Ark 15k so
> it can accept a single 4/0 cable and retain the full output capacity.
> Apparently, Homegrid is the only battery on the market with the output
> capacity to do this.
>
> https://www.homegridenergy.com/stackd-series
> <https://mailtrack.io/trace/link/a0cf1afc125652c2027c1cbd7d5458266a2d118b?url=https%3A%2F%2Fwww.homegridenergy.com%2Fstackd-series&userId=1613865&signature=28245d1e93ba151a>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
>
> On Thu, Jun 29, 2023 at 9:43 AM Lloyd Hoffstatter via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hi Maverick,
>>
>>
>>
>> Per tech support, you need to buss battery output(s) to both input
>> breakers to get the full 275 Amp output.
>>
>>
>>
>> Best regards,
>>
>> Lloyd
>>
>>
>>
>> Lloyd Hoffstatter, M.S. Applied Solar Energy
>>
>> NABCEP Inaugural Certified PV Installer Emeritus
>>
>> Director, Sunstruck Consulting
>>
>> Lloyd at SunstruckConsulting.com
>>
>> 845-657-8132 (office)
>>
>> 914-844-3404 (mobile)
>>
>>
>>
>> *From: *Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Sent: *Thursday, June 29, 2023 8:27 AM
>> *To: *RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Cc: *Mac Lewis <maclewis1 at gmail.com>
>> *Subject: *Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar
>>
>>
>>
>> Hi Jason,
>>
>>
>>
>> The Sol-Ark 15k has dual battery input terminals so they can be combined
>> right inside.  This could be a good option to consider.
>>
>>
>>
>> Thanks
>>
>>
>>
>>
>>
>> On Thu, Jun 29, 2023 at 6:17 AM Maverick Brown via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> I recommend the Victron Lynx Power In or the Lynx Distributor.
>>
>> Thank you,
>>
>>
>>
>> Maverick
>>
>>
>>
>>
>>
>> On Jun 29, 2023, at 6:55 AM, Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> 
>>
>> Hi all,
>>
>>
>>
>> I'm doing my first installation with two 24 kWh Homegrid stacks. They
>> will feed two Sol-Ark 15k. I'm seeking recommendations on busbars for
>> connecting this up in the most elegant way possible.
>>
>>
>>
>> Pictures speak 1,000 words, so if you have any I would appreciate it
>> (off-list is fine).
>>
>>
>>
>> Jason Szumlanski
>>
>> Florida Solar Design Group
>>
>>
>>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230629/0fe43286/attachment.htm>


More information about the RE-Wrenches mailing list