[RE-wrenches] Parallel Homegrid Stack'd Busbar
Jason Szumlanski
jason at floridasolardesigngroup.com
Thu Jun 29 16:32:50 EDT 2023
It looks like the Lynx Power In (without fuses like the Distributor) would
work in my application. In fact, it appears it can be accomplished with a
single unit, making it a pretty sleek and cost-effective solution.
I'll look into that and let you know what direction I went once it's all
installed. Thanks, all.
Jason Szumlanski
Florida Solar Design Group
On Thu, Jun 29, 2023 at 10:58 AM Peter Giroux via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Morning all
>
>
>
> You may also want to look at the Victron products. They have a 1000 amp
> version called the Lynx distributor.
>
>
>
> Peter Giroux
>
> ASAE
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Bradley Bassett via RE-wrenches
> *Sent:* Thursday, June 29, 2023 10:47 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Bradley Bassett <bbassett2 at gmail.com>
> *Subject:* Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar
>
>
>
> Note that MidNite now also makes 2000A and 500A versions of their BCB.
> With two Sol-Ark 15k you do need to use the 1000A version with 275A each
> inverter. I can also confirm that you do need to use both of the battery
> terminals in the Sol-Ark 15k for full power, or the Homegrid bus bars that
> Jason shows.
>
>
>
> Brad Bassett
>
>
>
>
>
> On Thu, Jun 29, 2023 at 6:57 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Lloyd,
>
>
>
> Homegrid makes a busbar to combine the two terminals in the Sol-Ark 15k so
> it can accept a single 4/0 cable and retain the full output capacity.
> Apparently, Homegrid is the only battery on the market with the output
> capacity to do this.
>
>
>
> https://www.homegridenergy.com/stackd-series
> <https://mailtrack.io/trace/link/a0cf1afc125652c2027c1cbd7d5458266a2d118b?url=https%3A%2F%2Fwww.homegridenergy.com%2Fstackd-series&userId=1613865&signature=28245d1e93ba151a>
>
>
> Jason Szumlanski
>
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
>
>
>
>
> On Thu, Jun 29, 2023 at 9:43 AM Lloyd Hoffstatter via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi Maverick,
>
>
>
> Per tech support, you need to buss battery output(s) to both input
> breakers to get the full 275 Amp output.
>
>
>
> Best regards,
>
> Lloyd
>
>
>
> Lloyd Hoffstatter, M.S. Applied Solar Energy
>
> NABCEP Inaugural Certified PV Installer Emeritus
>
> Director, Sunstruck Consulting
>
> Lloyd at SunstruckConsulting.com
>
> 845-657-8132 (office)
>
> 914-844-3404 (mobile)
>
>
>
> *From: *Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent: *Thursday, June 29, 2023 8:27 AM
> *To: *RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc: *Mac Lewis <maclewis1 at gmail.com>
> *Subject: *Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar
>
>
>
> Hi Jason,
>
>
>
> The Sol-Ark 15k has dual battery input terminals so they can be combined
> right inside. This could be a good option to consider.
>
>
>
> Thanks
>
>
>
>
>
> On Thu, Jun 29, 2023 at 6:17 AM Maverick Brown via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> I recommend the Victron Lynx Power In or the Lynx Distributor.
>
> Thank you,
>
>
>
> Maverick
>
>
>
>
>
> On Jun 29, 2023, at 6:55 AM, Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Hi all,
>
>
>
> I'm doing my first installation with two 24 kWh Homegrid stacks. They will
> feed two Sol-Ark 15k. I'm seeking recommendations on busbars for connecting
> this up in the most elegant way possible.
>
>
>
> Pictures speak 1,000 words, so if you have any I would appreciate it
> (off-list is fine).
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>