[RE-wrenches] Sol-Ark 15k

Michael Morningstar mjmorningstar at gmail.com
Mon May 9 23:06:40 EDT 2022


Sure, We are putting together a system w/ (8) Sol-Arks, (2) 400A transfer
Switches and (4) 400A load centers sitting on 10 x 10 gutters, No nipples
or raceways between them, we just cut a large portion of the bottoms or
tops out the enclosures with matching windows cut out of the gutters.
Nipples (Chase, Short, conduit and offset) are only used when absolutely
necessary. I will also use 2.5 x 2.5 wireways vertically in lieu of flex or
raceways. Internal and external elbows too. I've always designed electrical
rooms with the idea that the equipment will be swapped out in a decade or
two.  Also using a 20' long 10 x 10 gutter with 3/8 x 4" bussbars and 2.5 x
2.5" to connect 24 Discover AES's on this one. We'll have some pictures in
a month.

On Sun, May 8, 2022 at 1:38 PM Chris Sparadeo via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Michael, interesting idea! Mind sharing a photo so I can conceptualize
> better?
>
>
>
> On Sun, May 8, 2022 at 2:23 PM Jeff Clearwater via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> I've been using two gutters with multiple 12KW Sol-Arks Installs - one
>> 4x4" that I mount immediately under the AC KOs using forward biased offset
>> nipples (it's front face is just abouut 1/2" in front of front plane of
>> Sol-Arks)  and then a 6x6" set back and down and reached with 4" nipples
>> extending offset nipples so that I get an AC and DC gutter - not sure how
>> others are dealing with need to separate AC and DC.
>>
>> For the PV  inputs on 12Kws I do two additional 1" KOs - one through the
>> vertical mid-plate below the DC terminations and then one down through the
>> bottom just to the rear of that plate.  That way using offsets I can reach
>> the 6" DC gutter with both the Battery DC and the PV DC in one gutter.  I
>> then use an LL to get the AC gutter back to the wall at one end.  Can send
>> pics offlist if you are interested.
>>
>> I spoke to Sol-Ark a few times about the need to give us more room and
>> better KOs - putting the DCs in one plane and the ACS in another - giving
>> us 2" KOs for battery cables instead of forcing each cable through it's own
>> 1" etc.  Unfortunately didn't get that message through before they had
>> already designed the 15 KW.
>>
>> We have also just added KOs to the left side of the unit to bring in the
>> PV inputs when that is more convenient.
>>
>> No better tool than our hydraulic KO punch!
>>
>> Hope that helps ~
>>
>> Jeff
>>
>> ~~~~~~~~~~~
>> Jeff Clearwater
>>
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>> www.villagepowerdesign.com
>> cell - 413-559-9763
>> ~~~~~~~~~~~~~~~~~~~~~~~
>>
>>
>>
>>
>>
>> Michael Morningstar via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> May 8, 2022 at 11:03 AM
>> We cut out the bottom plate entirely with a die grinder/cut off wheel and
>> then wrap the raw edge with vinyl "edge wrap" and set the inverters on top
>> of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs
>> is screwy. Just need a bonding jumper between both enclosures. This is
>> common practice in the industrial world when dealing with large VFDs and
>> such.
>>
>>
>>
>>
>> --
>>
>> Michael Morningstar
>>
>>
>> Morningstar Electric
>>
>> PO Box 1494
>>
>> Mount Shasta, CA 96067
>>
>> 530-921-0560
>>
>> mjmorningstar at gmail.com
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> May 8, 2022 at 5:57 AM
>> Hi Chris,
>>
>> Can’t you increase the size of the KO’s?
>>
>> Jay
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> Chris Sparadeo via RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> May 7, 2022 at 6:16 PM
>> Jason,
>>
>> I think I agree with your interpretation of the wiring diagram. My
>> hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a
>> >24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe
>> to bend…and extra BOS seems like a less than ideal solution.
>>
>> Is this your conclusion as well?
>>
>> --
>> Chris Sparadeo
>>
>>
>> C_802-369-4458
>> H_802-728-3059
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> --
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220509/57850df2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: VPDLogoMaster2.jpg
Type: image/jpeg
Size: 93349 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220509/57850df2/attachment.jpg>


More information about the RE-Wrenches mailing list