<div dir="ltr">Sure, We are putting together a system w/ (8) Sol-Arks, (2) 400A transfer Switches and (4) 400A load centers sitting on 10 x 10 gutters, No nipples or raceways between them, we just cut a large portion of the bottoms or tops out the enclosures with matching windows cut out of the gutters. Nipples (Chase, Short, conduit and offset) are only used when absolutely necessary. I will also use 2.5 x 2.5 wireways vertically in lieu of flex or raceways. Internal and external elbows too. I&#39;ve always designed electrical rooms with the idea that the equipment will be swapped out in a decade or two.  Also using a 20&#39; long 10 x 10 gutter with 3/8 x 4&quot; bussbars and 2.5 x 2.5&quot; to connect 24 Discover AES&#39;s on this one. We&#39;ll have some pictures in a month.</div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 8, 2022 at 1:38 PM Chris Sparadeo via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto">Michael, interesting idea! Mind sharing a photo so I can conceptualize better?  </div><div dir="auto"><br></div><div dir="auto"><br></div><div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 8, 2022 at 2:23 PM Jeff Clearwater via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">

<div>I&#39;ve been using two gutters with multiple 
12KW Sol-Arks Installs - one 4x4&quot; that I mount immediately under the AC 
KOs using forward biased offset nipples (it&#39;s front face is just abouut 
1/2&quot; in front of front plane of Sol-Arks)  and then a 6x6&quot; set back and 
down and reached with 4&quot; nipples extending offset nipples so that I get 
an AC and DC gutter - not sure how others are dealing with need to 
separate AC and DC.  <br>
<br>
For the PV  inputs on 12Kws I do two additional 1&quot; KOs - one through the
 vertical mid-plate below the DC terminations and then one down through 
the bottom just to the rear of that plate.  That way using offsets I can
 reach the 6&quot; DC gutter with both the Battery DC and the PV DC in one 
gutter.  I then use an LL to get the AC gutter back to the wall at one 
end.  Can send pics offlist if you are interested.<br>
<br>
I spoke to Sol-Ark a few times about the need to give us more room and 
better KOs - putting the DCs in one plane and the ACS in another - 
giving us 2&quot; KOs for battery cables instead of forcing each cable 
through it&#39;s own 1&quot; etc.  Unfortunately didn&#39;t get that message through 
before they had already designed the 15 KW.<br>
<br>
We have also just added KOs to the left side of the unit to bring in the
 PV inputs when that is more convenient.<br>
<br>
No better tool than our hydraulic KO punch!<br>
<br>
Hope that helps ~<br>
<br>
Jeff<br>
<br>
<span>~~~~~~~~~~~<br>





</span>
<div>

  <span>Jeff Clearwater</span><span><span></span><br>
  <img src="cid:180a55fdfe12876bd9a1" style="width: 732px; max-width: 100%;"><br>
  </span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank">linkedin</a>
 </span></span></span><br>


  <span><span><a href="http://www.villagepowerdesign.com" target="_blank">www.villagepowerdesign.com</a></span><br>



















cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>
<br>
<br>
<br>
<br>
<span>

</span><br>
<blockquote type="cite" style="border:0px none">
  <div style="margin:30px 25px 10px"><div style="width:100%;border-top:2px solid rgba(146,154,163,0.7);padding-top:10px">   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%">
        <a style="padding-right:6px;font-weight:500;color:rgb(72,86,100);text-decoration:none" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">Michael Morningstar via RE-wrenches</a></div>   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:right">     <font style="color:rgb(144,154,164)"><span style="padding-left:6px">May 
8, 2022 at 11:03 AM</span></font></div>    </div></div>
  <div style="margin-left:24px;margin-right:24px;color:rgb(144,154,164)">
<div dir="ltr">We cut out the bottom plate entirely with a die grinder/cut 
off wheel and then wrap the raw edge with vinyl &quot;edge wrap&quot; and set the 
inverters on top of 10 x 10 x whatever gutters. The layout and sizes of 
Sol-Arks knock-outs is screwy. Just need a bonding jumper between both 
enclosures. This is common practice in the industrial world when dealing
 with large VFDs and such.<div><br></div></div><br><br clear="all"><div><br></div>--
 <br><div dir="ltr"><div dir="ltr">







<p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica;min-height:22px"><span style="font-family:Helvetica"></span></p>
<p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica">Michael Morningstar</p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica"><br></p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica">Morningstar Electric</p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica">PO Box 1494</p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica">Mount Shasta, CA 96067</p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica">530-921-0560</p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica"><a href="mailto:mjmorningstar@gmail.com" style="font-family:Helvetica" target="_blank">mjmorningstar@gmail.com</a></p><p style="margin:0px;font-style:normal;font-variant-caps:normal;font-weight:normal;font-stretch:normal;font-size:18px;line-height:normal;font-family:Helvetica"><img src="https://ci3.googleusercontent.com/mail-sig/AIorK4xkNeAOHZC3SDnZTmnhgML4JHyGwi0PdmG_TrSHASBRfwJtZqGi7vknpXAngaaiawfnr5xCF1Y" width="200" height="118" style="font-family: Helvetica;"><br></p></div></div>

<br><fieldset></fieldset><br><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>Pay optional member dues here: 
<a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: 
<a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address
 &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn&#39;t work, try the 
other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div>

  </div>
  <div style="margin:30px 25px 10px"><div style="width:100%;border-top:2px solid rgba(146,154,163,0.7);padding-top:10px">   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%">
        <a style="padding-right:6px;font-weight:500;color:rgb(72,86,100);text-decoration:none" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">Jay via RE-wrenches</a></div>   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:right">     <font style="color:rgb(144,154,164)"><span style="padding-left:6px">May 
8, 2022 at 5:57 AM</span></font></div>    </div></div>
  <div style="margin-left:24px;margin-right:24px;color:rgb(144,154,164)"><div dir="ltr">Hi Chris,</div><div dir="ltr"><br></div><div dir="ltr">Can\u2019t 
you increase the size of the KO\u2019s?</div><div dir="ltr"><br></div><div dir="ltr">Jay</div><div dir="ltr"><br></div>
<br><fieldset></fieldset><br><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>Pay optional member dues here: 
<a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: 
<a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address
 &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn&#39;t work, try the 
other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div>

  </div>
  <div style="margin:30px 25px 10px"><div style="width:100%;border-top:2px solid rgba(146,154,163,0.7);padding-top:10px">   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%">
        <a style="padding-right:6px;font-weight:500;color:rgb(72,86,100);text-decoration:none" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">Chris Sparadeo via RE-wrenches</a></div>   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:right">     <font style="color:rgb(144,154,164)"><span style="padding-left:6px">May 
7, 2022 at 6:16 PM</span></font></div>    </div></div>
  <div style="margin-left:24px;margin-right:24px;color:rgb(144,154,164)">
<div dir="auto">Jason,</div><div dir="auto"><br></div><div dir="auto">I think
 I agree with your interpretation of the wiring diagram. My hesitation 
is, with a 1-1/4\u201d KO for AC inputs, only choice seems to be a &gt;24\u201d 
stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe 
to bend\u2026and extra BOS seems like a less than ideal solution. </div><div dir="auto"><br></div><div dir="auto">Is this your conclusion as well? </div><div><br></div>--
 <br><div dir="ltr"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div>Chris Sparadeo</div><div><br></div><div><br></div><div>C_802-369-4458</div><div>H_802-728-3059</div></div></div></div></div></div>

<br><fieldset></fieldset><br><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>Pay optional member dues here: 
<a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: 
<a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address
 &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn&#39;t work, try the 
other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div>

  </div>
</blockquote>
<br>
<div>-- <br><span><span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)"></span></span></div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div>-- <br><div dir="ltr"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div>Chris Sparadeo</div><div><br></div><div><br></div><div>C_802-369-4458</div><div>H_802-728-3059</div><div></div></div></div></div></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr"><div dir="ltr">







<p style="margin:0px;font:18px Helvetica;min-height:22px"><span></span></p>
<p style="margin:0px;font:18px Helvetica">Michael Morningstar</p><p style="margin:0px;font:18px Helvetica"><br></p><p style="margin:0px;font:18px Helvetica">Morningstar Electric</p><p style="margin:0px;font:18px Helvetica">PO Box 1494</p><p style="margin:0px;font:18px Helvetica">Mount Shasta, CA 96067</p><p style="margin:0px;font:18px Helvetica">530-921-0560</p><p style="margin:0px;font:18px Helvetica"><a href="mailto:mjmorningstar@gmail.com" target="_blank">mjmorningstar@gmail.com</a></p><p style="margin:0px;font:18px Helvetica"><img width="200" height="118" src="https://ci3.googleusercontent.com/mail-sig/AIorK4xkNeAOHZC3SDnZTmnhgML4JHyGwi0PdmG_TrSHASBRfwJtZqGi7vknpXAngaaiawfnr5xCF1Y"><br></p></div></div>