[RE-wrenches] Sol-Ark install

scot.arey at solarcentex.com scot.arey at solarcentex.com
Wed Apr 13 07:29:51 EDT 2022


I agree with an earlier response…isn’t this a NABCEP PV Installation Professional-only forum?  The original question is DC-string design 101. Jerry is spot on for coldest temp adjustments, RSD considerations if required. But selecting a home run wire for separate string inputs to the inverter??? How can this be asked here?

Ron, are you NABCEP PV Installation Pro certified?

 

Scot Arey

Owner, Solar CenTex



 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jerry Shafer via RE-wrenches
Sent: Tuesday, April 12, 2022 10:27 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Jerry Shafer <jerrysgarage01 at gmail.com>
Subject: Re: [RE-wrenches] Sol-Ark install

 

Need more than this, we have amperage, we need distance, temp, # of wires per conduit, also at 480 you may want to verify cold temp for over the top voltage @ VOC, any RSD device(s) being used? Help to have total module count, as an example use a combiner to make 4 strings, 2 of equal voltage per input. For battery backup or off grid, Solark is the easiest you will get. 

Jerry

 NABCEP PV Inspector 

 

On Tue, Apr 12, 2022, 7:42 PM Ron Young via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> > wrote:

Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. Because the max DC voltage is 500v at 18a  and the PV I’m using is 40v DC each I will have to create three strings each 480v. What would be the best choice for a home run wire? I’ve always used smaller strings with micro inverters, a combiner at the array and a single Teck home run cable but the string inverter presents a different scenario and it looks like I’ll need to use three home run cables, one for each string. 

 

Ron Young

 

earthRight Products - Solareagle.com <http://Solareagle.com> 
Alternative Energy Solutions ~ Renewable Energy Products



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220413/002927dd/attachment.htm>


More information about the RE-Wrenches mailing list