[RE-wrenches] Sol-Ark install

Mac Lewis maclewis1 at gmail.com
Wed Apr 13 07:58:21 EDT 2022


Hello Ron,

I'll try to point you in the right direction here, but yes you want to move
forward cautiously.  Good training is easily available all over the place
now.  I will say that you can be an excellent and successful solar
installer these days without any experience with string inverters like
this.  MLPE has made this possible recently.

If this is on the roof, and you are on a 2014 NEC code or later, you will
need some type of module level or string level rapid shutdown device.  Tigo
seems to work well with the Sol-Ark built in RSS system.

As far as stringing, you need to apply your local climate's cold factor to
the Voc of the string, or use the module nameplate to figure out the true
Voc of each string and stay below the MPPT limit for Voc.  If you haven't
done this before, I would take a class. You can use Sol-Arks string
calculator here:
https://www.sol-ark.com/solar-panel-sizing/SolarPanelSizing.html

I always check any calculator's output by hand and verify that the Voc goes
up as temperature goes down.  This step should not be overlooked because
you can damage the MPPTs input.  The cold temp factor here in Colorado can
drive the Voc to 25% above the nameplate ratings, so don't ignore this.

Once you have your maximum string length, you want to figure out how to
wire this in as efficiently as possible.  You can combine 2 strings per
MPPT typically, but these parallel strings need to be the same number of
modules.  You also want the strings to face ~ same direction and have
similar shading characteristics for the most efficient operation over time.

Be careful and good luck!

On Wed, Apr 13, 2022 at 5:29 AM Scot Arey via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> I agree with an earlier response…isn’t this a NABCEP PV Installation
> Professional-only forum?  The original question is DC-string design 101.
> Jerry is spot on for coldest temp adjustments, RSD considerations if
> required. But selecting a home run wire for separate string inputs to the
> inverter??? How can this be asked here?
>
> Ron, are you NABCEP PV Installation Pro certified?
>
>
>
> Scot Arey
>
> Owner, Solar CenTex
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jerry Shafer via RE-wrenches
> *Sent:* Tuesday, April 12, 2022 10:27 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jerry Shafer <jerrysgarage01 at gmail.com>
> *Subject:* Re: [RE-wrenches] Sol-Ark install
>
>
>
> Need more than this, we have amperage, we need distance, temp, # of wires
> per conduit, also at 480 you may want to verify cold temp for over the top
> voltage @ VOC, any RSD device(s) being used? Help to have total module
> count, as an example use a combiner to make 4 strings, 2 of equal voltage
> per input. For battery backup or off grid, Solark is the easiest you will
> get.
>
> Jerry
>
>  NABCEP PV Inspector
>
>
>
> On Tue, Apr 12, 2022, 7:42 PM Ron Young via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install.
> Because the max DC voltage is 500v at 18a  and the PV I’m using is 40v DC
> each I will have to create three strings each 480v. What would be the best
> choice for a home run wire? I’ve always used smaller strings with micro
> inverters, a combiner at the array and a single Teck home run cable but the
> string inverter presents a different scenario and it looks like I’ll need
> to use three home run cables, one for each string.
>
>
>
> Ron Young
>
>
>
> earthRight Products - Solareagle.com
> Alternative Energy Solutions ~ Renewable Energy Products
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220413/c06c7127/attachment.htm>


More information about the RE-Wrenches mailing list