[RE-wrenches] Sol-Ark install
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Apr 12 23:27:16 EDT 2022
Need more than this, we have amperage, we need distance, temp, # of wires
per conduit, also at 480 you may want to verify cold temp for over the top
voltage @ VOC, any RSD device(s) being used? Help to have total module
count, as an example use a combiner to make 4 strings, 2 of equal voltage
per input. For battery backup or off grid, Solark is the easiest you will
get.
Jerry
NABCEP PV Inspector
On Tue, Apr 12, 2022, 7:42 PM Ron Young via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install.
> Because the max DC voltage is 500v at 18a and the PV I’m using is 40v DC
> each I will have to create three strings each 480v. What would be the best
> choice for a home run wire? I’ve always used smaller strings with micro
> inverters, a combiner at the array and a single Teck home run cable but the
> string inverter presents a different scenario and it looks like I’ll need
> to use three home run cables, one for each string.
>
> Ron Young
>
> earthRight Products - Solareagle.com
> Alternative Energy Solutions ~ Renewable Energy Products
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220412/810e7ebc/attachment.htm>
More information about the RE-Wrenches
mailing list