[RE-wrenches] Equipment for 400 Amp Service Supply Side & 2 200s

August Goers august at luminalt.com
Tue Mar 29 14:59:08 EDT 2022


Hi Jeff -

There is no particular supply side connection location on this panel - I
think if you needed that it is best to go with the Siemens part that
Vincent sent over.

However, you could use the sum of all breakers rule on the internal bus and
install up to 200 A of solar breakers in the panel. Then, use the other 200
A main breaker to feed your loads. If your loads are larger than 200 A, I
suppose this won't work.

August


On Tue, Mar 29, 2022 at 11:43 AM Jeff Clearwater <
jeffc at villagepowerdesign.com> wrote:

> Thanks August yes but am I missing where you put the third tap for the PV
> backfeed?  I need 2 x 200 amp mains plus a 200 amp pv backfees point and
> the meter needs to have test bypass links.
>
> Sent from my iPhone
>
> On Mar 29, 2022, at 10:34 AM, August Goers <august at luminalt.com> wrote:
>
> 
> Hi Jeff -
>
> There are several 400 A (or 320 A continuous) meter/mains on the market
> with 2 x 200 A breakers. In the Bay Area these are frequently referred to
> as "California 400" panels, even though they are installed with a self
> contained 320 A rated utility meter, rather than a 400 A CT-meter. They are
> great for systems with large energy storage, because one 200 A breaker can
> feed non-backup loads and the other 200 A breaker can feed backup loads and
> solar.  Anyway, here's one such example:
>
> https://www.milbankworks.com/products/catalog/M400-UG-APS-LC
>
> Best,
>
> August
> Luminalt
>
>
> On Tue, Mar 29, 2022 at 10:15 AM Jeff Clearwater via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Good Day Wrenches,
>>
>> Does anyone know of a 400 Amp Meter/Main that can accomplish the
>> following?
>>
>> 1)  Provide 2 x 200 Main Breakers for Loads
>> 2) Provide an easy supply side tap point for 160 Amps of Grid-tie Solar
>> (so basically a 200 Amp backfeed)
>>
>> I'm considering using an Eaton 324 N
>> <https://www.rexelusa.com/p/525405/eaton-b-line/400a-4p-4-jaw-meter-socket/782051622102/324-n>
>> (Eaton B-Line 324 N 400A, 320 A cont. 4P, 4 Jaw, Meter Socket W Link Bypass
>> Facilities) but I'm not sure I can double lug it and then also tap off of
>> one of the 200 Amp lines with another tap (using Ilsco IPC-250-4/0
>> <https://www.ilsco.com/Ilsco/ccrz__ProductDetails?sku=IPC-250-4%2F0-ILSM-ILS&cclcl=en_US>
>> splice connectors).
>>
>> Thanks!
>>
>> Jeff
>>
>>
>> ~~~~~~~~~~~
>> Jeff Clearwater
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>>
>> <VPDLogoMaster2.jpeg>
>>
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>> www.villagelab.net
>> www.villagepowerdesign.com
>> cell - 413-559-9763
>> ~~~~~~~~~~~~~~~~~~~~~~~
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220329/0e7d03b5/attachment.htm>


More information about the RE-Wrenches mailing list