[RE-wrenches] Equipment for 400 Amp Service Supply Side & 2 200s
Jeff Clearwater
jeffc at villagepowerdesign.com
Tue Mar 29 14:43:51 EDT 2022
Thanks August yes but am I missing where you put the third tap for the PV backfeed? I need 2 x 200 amp mains plus a 200 amp pv backfees point and the meter needs to have test bypass links.
Sent from my iPhone
> On Mar 29, 2022, at 10:34 AM, August Goers <august at luminalt.com> wrote:
>
>
> Hi Jeff -
>
> There are several 400 A (or 320 A continuous) meter/mains on the market with 2 x 200 A breakers. In the Bay Area these are frequently referred to as "California 400" panels, even though they are installed with a self contained 320 A rated utility meter, rather than a 400 A CT-meter. They are great for systems with large energy storage, because one 200 A breaker can feed non-backup loads and the other 200 A breaker can feed backup loads and solar. Anyway, here's one such example:
>
> https://www.milbankworks.com/products/catalog/M400-UG-APS-LC
>
> Best,
>
> August
> Luminalt
>
>
>> On Tue, Mar 29, 2022 at 10:15 AM Jeff Clearwater via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>> Good Day Wrenches,
>>
>> Does anyone know of a 400 Amp Meter/Main that can accomplish the following?
>>
>> 1) Provide 2 x 200 Main Breakers for Loads
>> 2) Provide an easy supply side tap point for 160 Amps of Grid-tie Solar (so basically a 200 Amp backfeed)
>>
>> I'm considering using an Eaton 324 N (Eaton B-Line 324 N 400A, 320 A cont. 4P, 4 Jaw, Meter Socket W Link Bypass Facilities) but I'm not sure I can double lug it and then also tap off of one of the 200 Amp lines with another tap (using Ilsco IPC-250-4/0 splice connectors).
>>
>> Thanks!
>>
>> Jeff
>>
>>
>> ~~~~~~~~~~~
>> Jeff Clearwater
>> linkedin
>>
>> <VPDLogoMaster2.jpeg>
>>
>> linkedin
>> www.villagelab.net
>> www.villagepowerdesign.com
>> cell - 413-559-9763
>> ~~~~~~~~~~~~~~~~~~~~~~~
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220329/a1ddec6f/attachment.htm>
More information about the RE-Wrenches
mailing list