Thanks, The GSLC spec sheet does not mention the breaker assembly is
included, unless I missed it, I'll have to verify with OB, I was wondering
about this. Lones from OB, if you are reading this, can you comment?

On Tue, Mar 1, 2022 at 10:34 AM Bradley Bassett <bbassett2 at gmail.com> wrote:

> I think the blank GSLC comes with the main breaker bracket and the bus
> bars for connecting them. What I have not had a chance to try is connecting
> the breaker bus that usually connects the bottom of the two main breakers
> directly to the upper bus bars, and not installing the two breakers at all.
> It seems like it would fit, but until I see it done I would not specify it.
> I've often specified a single 250A breaker, usually in a MidNite BCB, to
> each inverter so that a single 4/0 cable can be used to each inverter. I've
> been specifying this since the Radian came out and have had no reports of
> the breaker tripping. This keeps the necessary bus bar size for multiple
> inverters at a lower rating. Four inverters can be kept within the 1000A
> rating of the MidNite BCB and the 1000A shunt can be used for the FNDC. If
> you put all of the charge controllers in a FW500 or FW1000 you can use
> those shunts for the solar to the FNDC.
>
> Brad B
> AEE Solar
>
> On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <kirkh at vermont.solar> wrote:
>
>> All,
>>
>> I am doing a multiple stacked Radian GS8048 system. And all I need in my
>> design is two OB 175 a breakers in a box which integrates w/ each
>> respective inverter. The manual bypass switch is useless, for all inverters
>> need to be bypassed at once using a single external bypass. OB does not
>> make a version of the GSLC which only has the inverter breakers. They do
>> make an empty GSLC with nothing in it. But no mounting assembly for the
>> breakers, and no add-on kit offering to do this either.
>> I thought Midnite made something compatible, but don't see it on their
>> web site. Any ideas? Thanks.
>>
>> --
>>
>> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>>
>> *Owner|Principal, VT Solar, LLC*
>>
>> *Celebrating our 31st Anniversary 1991-2022!!*
>>
>> *www.vermont.solar*
>> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>>
>> dba Vermont Solar Engineering
>>
>> 802.863.1202
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>

dba Vermont Solar Engineering

802.863.1202
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220301/980f3910/attachment.htm>


More information about the RE-Wrenches mailing list