[RE-wrenches] Outback Radian transfer time

jay jay.peltz at gmail.com
Fri Feb 4 17:05:17 EST 2022


HI Eric,

Check that the transfer delay is as short as it can go, about 6 cycles

You might raise the lower voltage limit from 108

Check to make sure all the voltage readings on each inverter are as close as possible.  A real weakness of the OB platform is that you have to calibrate each item:  

And depending on how you have the power save mode configured, if might be that if you can get the generator to drop out with just 1 inverter active that might eliminate the transfer delay issues.

Let us know what you find.

jay





> On Feb 4, 2022, at 7:48 AM, Eric Smiley <eric at vecoop.ca> wrote:
> 
> I have an off grid system with three GS8048A inverters. 
> Every time it switches from generator charging to inverting - at the end of absorption - the lights flicker and a propane boiler in the house goes into fault. 
> I'm using Advanced AGS on the Mate3S.
> 
> The loads don't exceed about 6 kW right now.
> 
> Does anyone know if there's a way to reduce the transfer time? The transition to charging is smooth. I don't understand why it's so clunky transitioning back to inverting.
> 
> 
> Eric Smiley
> Project Manager, North Island
> 
> E:  eric at vecoop.ca <mailto:eric at vecoop.ca>
> T:  1-888-386-0116 ext 702 (toll free)
> C:  250-703-6004
> W:  viridianenergy.ca <http://viridianenergy.ca/>_______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220204/8b601f9c/attachment.htm>


More information about the RE-Wrenches mailing list