Not sure about the radians (I've rarely used them) but with the VFX series,
that symptom can sometimes be avoided by programming a cool down period so
that the inverters drop the generator while it is still running at full
speed.  Alternatively, by narrowing the generator voltage window at the
bottom end, the inverters will potentially drop the generator connection
before the voltage output gets too low as the generator shuts down.
Hope this helps,
Howie

*Howie Michaelson**Sun Catcher*

*NABCEP Certified Solar PV Installerâ„¢*

*Solar Electric Systems Sales & Service802-272-0004*


On Fri, Feb 4, 2022 at 9:49 AM Eric Smiley <eric at vecoop.ca> wrote:

> I have an off grid system with three GS8048A inverters.
> Every time it switches from generator charging to inverting - at the end
> of absorption - the lights flicker and a propane boiler in the house goes
> into fault.
> I'm using Advanced AGS on the Mate3S.
>
> The loads don't exceed about 6 kW right now.
>
> Does anyone know if there's a way to reduce the transfer time? The
> transition to charging is smooth. I don't understand why it's so clunky
> transitioning back to inverting.
>
>
> Eric Smiley
> Project Manager, North Island
>
> E:  eric at vecoop.ca
> T:  1-888-386-0116 ext 702 (toll free)
> C:  250-703-6004
> W:  viridianenergy.ca
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220204/bb9268ae/attachment.htm>


More information about the RE-Wrenches mailing list