<html><head><meta http-equiv="Content-Type" content="text/html; charset=us-ascii"></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; line-break: after-white-space;" class="">HI Eric,<div class=""><br class=""></div><div class="">Check that the transfer delay is as short as it can go, about 6 cycles</div><div class=""><br class=""></div><div class="">You might raise the lower voltage limit from 108</div><div class=""><br class=""></div><div class="">Check to make sure all the voltage readings on each inverter are as close as possible. &nbsp;A real weakness of the OB platform is that you have to calibrate each item: &nbsp;</div><div class=""><br class=""></div><div class="">And depending on how you have the power save mode configured, if might be that if you can get the generator to drop out with just 1 inverter active that might eliminate the transfer delay issues.</div><div class=""><br class=""></div><div class="">Let us know what you find.</div><div class=""><br class=""></div><div class="">jay</div><div class=""><br class=""></div><div class=""><br class=""></div><div class=""><br class=""></div><div class=""><br class=""></div><div class=""><div><br class=""><blockquote type="cite" class=""><div class="">On Feb 4, 2022, at 7:48 AM, Eric Smiley &lt;<a href="mailto:eric@vecoop.ca" class="">eric@vecoop.ca</a>&gt; wrote:</div><br class="Apple-interchange-newline"><div class=""><div dir="auto" class="">I have an off grid system with three GS8048A inverters.&nbsp;<div dir="auto" class="">Every time it switches from generator charging to inverting - at the end of absorption - the lights flicker and a propane boiler in the house goes into fault.&nbsp;</div><div dir="auto" class="">I'm using Advanced AGS on the Mate3S.</div><div dir="auto" class=""><br class=""></div><div dir="auto" class="">The loads don't exceed about 6 kW right now.</div><div dir="auto" class=""><br class=""></div><div dir="auto" class="">Does anyone know if there's a way to reduce the transfer time? The transition to charging is smooth. I don't understand why it's so clunky transitioning back to inverting.</div><div dir="auto" class=""><br class=""></div><div dir="auto" class=""><br class=""><div data-smartmail="gmail_signature" dir="auto" class="">Eric Smiley<br class="">Project Manager, North Island<br class=""><br class="">E: &nbsp;<a href="mailto:eric@vecoop.ca" class="">eric@vecoop.ca</a><br class="">T: &nbsp;1-888-386-0116 ext 702 (toll free)<br class="">C: &nbsp;250-703-6004<br class="">W: &nbsp;<a href="http://viridianenergy.ca/" class="">viridianenergy.ca</a></div></div></div>
_______________________________________________<br class="">List sponsored by Redwood Alliance<br class=""><br class="">Pay optional member dues here: <a href="http://re-wrenches.org" class="">http://re-wrenches.org</a><br class=""><br class="">List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" class="">RE-wrenches@lists.re-wrenches.org</a><br class=""><br class="">Change listserver email address &amp; settings:<br class=""><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" class="">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br class=""><br class="">There are two list archives for searching. When one doesn't work, try the other:<br class="">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<br class="">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br class=""><br class="">List rules &amp; etiquette:<br class="">http://www.re-wrenches.org/etiquette.htm<br class=""><br class="">Check out or update participant bios:<br class="">http://www.members.re-wrenches.org<br class=""><br class=""></div></blockquote></div><br class=""></div></body></html>