[RE-wrenches] neutral sizing for sense
Dave Tedeyan
dave at sungineersolar.com
Tue Jan 25 09:24:00 EST 2022
Drake,
I believe that is for a single phase 2 wire output only. I am assuming one
hot and one neutral for the inverter output in this case. I would think
most *grid tied* inverters fall under 705.95B, where the neutral is only a
voltage sense and can be sized as small as the equipment ground.
Cheers,
Dave
On Tue, Jan 25, 2022, 8:37 AM <drake.chamberlin at redwoodalliance.org> wrote:
> "the maximum load connected between the neutral and any one ungrounded
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ungrounded> conductor
> plus the inverter
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/6/special-equipment#inverter> output
> rating shall not exceed the ampacity
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ampacity> of
> the neutral conductor
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#neutral_conductor>
> ."
>
>
> So the neutral conductor is supposed to be sized for the connected load
> plus the entire maximum output of the inverter?
> ---
>
>
>
> On 2022-01-24 12:10, Kirk Herander wrote:
>
> 705.95 Ampacity of Neutral Conductor
> National Electrical Code 2017 of New York State
> <https://up.codes/viewer/new_york/nfpa-70-2017> > 7 Special Conditions
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#7>
> > 705 Interconnected Electric Power Production Sources
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#705>
> > 705.95 Ampacity of Neutral Conductor
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#705.95>
> JUMP TO FULL CODE CHAPTER
>
> The ampacity
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ampacity> of
> the neutral conductors
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#neutral_conductor> shall
> comply with either (A) or (B).
>
>
> (A) Neutral Conductor for Single Phase, 2-Wire Inverter Output
> <#m_3695074346584270383_NOP>
>
> If a single-phase, 2-wire
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/8/communications-systems#wire>
> inverter
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/6/special-equipment#inverter> output
> is connected to the neutral and one ungrounded
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ungrounded> conductor
> (only) of a 3-wire
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/8/communications-systems#wire> system
> or of a 3-phase, 4-wire
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/8/communications-systems#wire>,
> wye-connected system, the maximum load connected between the neutral and
> any one ungrounded
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ungrounded> conductor
> plus the inverter
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/6/special-equipment#inverter> output
> rating shall not exceed the ampacity
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ampacity> of
> the neutral conductor
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#neutral_conductor>
> .
>
>
> (B) Neutral Conductor for Instrumentation, Voltage, Detection or Phase
> Detection <#m_3695074346584270383_NOP>
>
> A conductor used solely for instrumentation, voltage
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#voltage_of_a_circuit> detection,
> or phase detection and connected to a single-phase or 3-phase interactive
> inverter
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#interactive_inverter>,
> shall be permitted to be sized at less than the ampacity
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ampacity> of
> the other current-carrying conductors and shall be sized equal to or larger
> than the equipment grounding conductor
> <https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#grounding_conductor_equipment_egc>
> .
>
> On Mon, Jan 24, 2022 at 11:58 AM Foxfire Energy <dan at foxfire-energy.com>
> wrote:
>
> I'd start with the manufacturers recommendations
>
> Sent from my iPhone
>
> > On Jan 24, 2022, at 11:52 AM, jay <jay.peltz at gmail.com> wrote:
> >
> > HI All,
> >
> > Where do I find in the code how to size a sense only neutral wire for GT
> inverter.
> >
> > thanks
> >
> > jay
> >
> > peltz power
> >
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > Pay optional member dues here: http://re-wrenches.org
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > There are two list archives for searching. When one doesn't work, try
> the other:
> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > http://www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > http://www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 31st Anniversary 1991-2022!!*
>
> *www.vermont.solar*
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220125/22a1eb2f/attachment.htm>
More information about the RE-Wrenches
mailing list