[RE-wrenches] neutral sizing for sense
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Tue Jan 25 08:37:34 EST 2022
"the maximum load connected between the neutral and any one ungrounded
[10] conductor plus the inverter [9] output rating shall not exceed the
ampacity [5] of the neutral conductor [6]."
So the neutral conductor is supposed to be sized for the connected load
plus the entire maximum output of the inverter?
---
On 2022-01-24 12:10, Kirk Herander wrote:
> 705.95 AMPACITY OF NEUTRAL CONDUCTOR
>
> National Electrical Code 2017 of New York State [1] > 7 Special Conditions [2] > 705 Interconnected Electric Power Production Sources [3] > 705.95 Ampacity of Neutral Conductor [4]
> JUMP TO FULL CODE CHAPTER
>
> The ampacity [5] of the neutral conductors [6] shall comply with either (A) or (B).
>
> (A) NEUTRAL CONDUCTOR FOR SINGLE PHASE, 2-WIRE INVERTER OUTPUT [7]
>
> If a single-phase, 2-wire [8] inverter [9] output is connected to the neutral and one ungrounded [10] conductor (only) of a 3-wire [8] system or of a 3-phase, 4-wire [8], wye-connected system, the maximum load connected between the neutral and any one ungrounded [10] conductor plus the inverter [9] output rating shall not exceed the ampacity [5] of the neutral conductor [6].
>
> (B) NEUTRAL CONDUCTOR FOR INSTRUMENTATION, VOLTAGE, DETECTION OR PHASE DETECTION [7]
>
> A conductor used solely for instrumentation, voltage [11] detection, or phase detection and connected to a single-phase or 3-phase interactive inverter [12], shall be permitted to be sized at less than the ampacity [5] of the other current-carrying conductors and shall be sized equal to or larger than the equipment grounding conductor [13].
>
> On Mon, Jan 24, 2022 at 11:58 AM Foxfire Energy <dan at foxfire-energy.com> wrote:
>
>> I'd start with the manufacturers recommendations
>>
>> Sent from my iPhone
>>
>>> On Jan 24, 2022, at 11:52 AM, jay <jay.peltz at gmail.com> wrote:
>>>
>>> HI All,
>>>
>>> Where do I find in the code how to size a sense only neutral wire for GT inverter.
>>>
>>> thanks
>>>
>>> jay
>>>
>>> peltz power
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>
> --
>
> Kirk Herander / kirkh at vermont.solar
>
> Owner|Principal, VT Solar, LLC
>
> _Celebrating our 31st Anniversary 1991-2022!!_
>
> www.vermont.solar [14]
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] https://up.codes/viewer/new_york/nfpa-70-2017
[2]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#7
[3]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#705
[4]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/7/special-conditions#705.95
[5]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ampacity
[6]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#neutral_conductor
[7] http://webmail.redwoodalliance.org/./#NOP
[8]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/8/communications-systems#wire
[9]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/6/special-equipment#inverter
[10]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#ungrounded
[11]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#voltage_of_a_circuit
[12]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#interactive_inverter
[13]
https://up.codes/viewer/new_york/nfpa-70-2017/chapter/1/general#grounding_conductor_equipment_egc
[14]
https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220125/d59fd9f0/attachment.htm>
More information about the RE-Wrenches
mailing list