Hello Wrenches
I was able to contact Mac this morning. Luckily this system was on optics so we were able to go look at the start and stop conditions in the AGS programming and the Event logs.
The event logs stated the stop was caused by an SOC stop command.
In AGS this system is using 3 start conditions
Voltage start , Load start and Soc start
At the customer’s request the Soc is set to start at 82 % and stop at 90%
Which seems a little crazy to both Mac and I
But to test if the Soc was indeed the cause of the short run.
We disabled the SOC start/stop.
We then started a bulk cycle to set the absorb timer to the 2 hr time limit as programmed in the inverter.
We raised the 2 minute timer above the current battery voltage to initiate a gen run.
The gen did start and at this point the gen has run for approximately 1.5 to 2 hours.
So it does appear that SOC stop was the cause of the short run, as indicated in the event Log.
What neither or Mac or myself can explain is the graph on the Dashboard does not show the Soc above
80% I am not certain if it is due to a momentary spike that is too quick to record. At this point that is just a guess (sorry). But that is the situation.
I will say it was nice to have this on Optics as we could go visit the site and do everything from our respective homes.
Mac thank you for returning my call and working through this issue.
Take Care All
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Mac Lewis
Sent: Thursday, January 13, 2022 4:38 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Radian Glitch
CAUTION: This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe.
Good Morning Wrenches,
I have an Outback Radian 8048 site that is acting up.
This only happens when the generator is automatically started.
It will start the generator and warm it up normally and then connect and start charging as it should. After about 30 seconds to 1 minute it will drop the AC input, and put the generator in cool down mode and the charger will be disabled. It will then continue to run the generator until you turn it off manually, presumably because it hasn't reached the stop trigger.
This system will charge normally when the generator is manually started. The firmware on the Mate3s is up to date.
Any ideas?
Thanks in advance
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220113/03d80108/attachment.htm>
More information about the RE-Wrenches
mailing list