[RE-wrenches] Radian Glitch
Howie Michaelson
Howie.Michaelson at gmail.com
Thu Jan 13 17:42:14 EST 2022
Thanks for the update Lines. While it seems from turning off the soc gen
control, the generator is running as it should, I don't understand how that
explains the charging behavior, or why the inverter continued to ruin the
generator without using it's output.
Howie
Howie Michaelson
Sun Catcher
NABCEP Certified Solar PV Installer™
Solar Electric & Heat Pumps Systems Sales & Service
802-272-0004
On Thu, Jan 13, 2022, 1:32 PM Tuss, Lones <lones.tuss at enersys.com> wrote:
> Hello Wrenches
>
> I was able to contact Mac this morning. Luckily this system was on optics
> so we were able to go look at the start and stop conditions in the AGS
> programming and the Event logs.
>
> The event logs stated the stop was caused by an SOC stop command.
>
> In AGS this system is using 3 start conditions
>
> Voltage start , Load start and Soc start
>
> At the customer’s request the Soc is set to start at 82 % and stop at 90%
>
> Which seems a little crazy to both Mac and I
>
> But to test if the Soc was indeed the cause of the short run.
>
> We disabled the SOC start/stop.
>
> We then started a bulk cycle to set the absorb timer to the 2 hr time
> limit as programmed in the inverter.
>
> We raised the 2 minute timer above the current battery voltage to initiate
> a gen run.
>
> The gen did start and at this point the gen has run for approximately 1.5
> to 2 hours.
>
> So it does appear that SOC stop was the cause of the short run, as
> indicated in the event Log.
>
> What neither or Mac or myself can explain is the graph on the Dashboard
> does not show the Soc above
>
> 80% I am not certain if it is due to a momentary spike that is too quick
> to record. At this point that is just a guess (sorry). But that is the
> situation.
>
> I will say it was nice to have this on Optics as we could go visit the
> site and do everything from our respective homes.
>
> Mac thank you for returning my call and working through this issue.
>
> Take Care All
>
>
>
>
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Mac Lewis
> *Sent:* Thursday, January 13, 2022 4:38 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Radian Glitch
>
>
>
> *CAUTION:* This email originated from outside of the Company. Do not
> click links or open attachments unless you recognize the sender and know
> the content is safe.
>
>
>
> Good Morning Wrenches,
>
>
>
> I have an Outback Radian 8048 site that is acting up.
>
>
>
> This only happens when the generator is automatically started.
>
> It will start the generator and warm it up normally and then connect and
> start charging as it should. After about 30 seconds to 1 minute it will
> drop the AC input, and put the generator in cool down mode and the charger
> will be disabled. It will then continue to run the generator until you
> turn it off manually, presumably because it hasn't reached the stop
> trigger.
>
>
>
> This system will charge normally when the generator is manually started.
> The firmware on the Mate3s is up to date.
>
>
>
> Any ideas?
>
>
>
> Thanks in advance
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
>
>
> This email and any attachments may contain confidential information that
> is intended only for the recipient(s). If you have received this email in
> error, please notify the sender and delete it from your system. Any views
> or opinions presented in this email are solely those of the author and do
> not necessarily represent those of the company or its affiliates. This
> email does not constitute an agreement to conduct transactions by
> electronic means and does not create any legally binding contract or
> enforceable obligation in the absence of a fully signed written contract.
> The recipient should check this email and any attachments for viruses. The
> company accepts no liability for any loss or damage caused by software
> viruses. If you are the intended recipient and you do not wish to receive
> similar email(s) from us in the future then please notify the sender.
> Please consider the environment before printing.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220113/61c7f7aa/attachment.htm>
More information about the RE-Wrenches
mailing list