Thanks! I thought this was for Offgrid and that was my mistake. 

Will
it run a 15A table saw without losing power, or was that just too much
expertise? I will wait 3 years on anything that is suppose to replace what
I already use. I have a low opinion of the all in one for Offgrid anyways.
Especially a non low frequency design. Maybe time will change my opinion.
Thanks for the info!  

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060

On Fri, 7 May 2021 17:48:59 -0700, Jeff Clearwater 
wrote:  Dave A. - Sol-Arks' "GEN" breaker can be used for 1 of 3 operations
only - Generator, AC Coupling OR Smart Load (Load Shedding) So when you are
grid-interactive (which takes up your GRID breaker) and you have PV and a
Generator - the way to go is to have no AC Coupling - put the Grid and Gen
where they belong and enjoy the high efficiency and smart control of DC
Coupling, Time of Use control (for the Genny,the Grid and the Batteries) -
all in the mid to high 90's efficiency that the Sol-Ark provides.

 I know
Dave T that you already have an installed Enphase system that probably
needs to be Rapid Shutdown compliant as well AND that you have a whole
house genny - however - I still would take a strong look at the economic
tradeoffs of rewiring the array to DC - (could install Tigo RS) - and
splitting the whole house Gen output to the Sol-Ark and probably existing
Transfer switch. We are just saying - now you are utilizing your equipment
to the max! May not be economically feasible labor and additional hardware
wise in this situation. But I surely would do the math and look at that
tradeoff seriously - perhaps give that option to your customer to make the
economic decision - would result in long term happy customer and most
energy utilized with least fuel costs.

 I'll let that case rest! Gees! all
you asked for was some relay advice! See what you get with this List!? too
much expertise! :)

 Have fun,

 Jeff C.
 Village Power Design

    Dave
Angelini Offgrid Solar [3] May 7, 2021 at 3:25 PM    

I do not know much
about Sol-Arc, but one can AC couple and DC couple with a Radian or XW. The
genset is on the genset input where it belongs. 

For Offgrid AC coupling
is just another way to damage a battery or genset that does not need to be
there. I suppose in a really large microgrid with many houses and a skilled
person on site, it could be used as a second best method to DC coupling
everything.    Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [4]
e-mail offgridsolar at sti.net
[5]
text 209 813 0060  

On Fri, 7 May 2021 12:21:14 -0400, Jason
Szumlanski  [6] wrote: 


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [7]

List
Address: RE-wrenches at lists.re-wrenches.org [8]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[9]

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[10]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[11]

List rules ">  Jason Szumlanski [14] May 7, 2021 at 9:21 AM    I like
the idea of some small amount of AC Coupled PV for off-grid systems when
there is a known consistent daytime load. Around here the worst case
scenario involves afternoon air conditioning in summer, so some WSW-facing
AC coupled PV is an efficient way to cover that load and go into darkness
with full batteries.   If I understand things correctly, with a Sol-Ark you
can simultaneously do AC coupling on the GEN input and DC coupling on the
MPPTs and use the GRID input for the generator.    Jason    


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [15]

List
Address: RE-wrenches at lists.re-wrenches.org [16]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[17]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[18]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[19]

List rules ">  Dave Tedeyan [22] May 7, 2021 at 8:41 AM    I would
certainly agree with you all that AC coupled for off-grid is not the best
design choice. But just for clarification, this is a grid-tied system where
there is already an Enphase M215 system and a whole house generator set up.
Cheers,  Dave  

   -- 
   DAVE TEDEYAN, PE 
 1653 Slaterville Road,
Ithaca, NY 14850 Cell: 607-288-2898 www.sungineersolar.com [23]    


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [24]

List
Address: RE-wrenches at lists.re-wrenches.org [25]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[26]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[27]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[28]

List rules ">  Jerry Shafer [31] May 7, 2021 at 8:10 AM    I have to
agree with Dave on this, complex and off grid generally are not good
together, l sugest backing up and you might consider a redesign, dump
enphase, go directly in to the inverter DC side, now a gen set back up will
work. Your spending more time and effort going in a bad direction. AC
coupling for resi is not a great solution to start with and Solark even say
that. KISS is better Jerry NABCEP PV Inspector   


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [32]

List
Address: RE-wrenches at lists.re-wrenches.org [33]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[34]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[35]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[36]

List rules ">  Dave Angelini Offgrid Solar [39] May 6, 2021 at 7:33
AM    

I would not do any of this for an offgrid client. It is against the
rule of less is more. The whole design is flawed in my opinion.    Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [40]
e-mail
offgridsolar at sti.net [41]
text 209 813 0060  

On Tue, 4 May 2021 19:24:13
-0400, Dave Tedeyan  [42] wrote: 


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [43]

List
Address: RE-wrenches at lists.re-wrenches.org [44]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[45]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[46]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[47]

List rules ">  Dave Tedeyan [50] May 4, 2021 at 4:24 PM    I suppose
the question here is - which is the worse failure mode? A. Solar turning
off until an electrician can fix it. OR B. Not knowing the contactor failed
until it does not open when the generator turns on and running the risk
that the solar backfeeds the generator and breaks it.   For off-grid maybe
A would be more of a concern. But for grid tied, I would think option B
would be worse.   Does anyone have a fail safe method of doing this?  
Cheers, Dave  

 _______________________________________________
List
sponsored by Redwood Alliance

Pay optional member dues here:
http://re-wrenches.org [51]

List Address:
RE-wrenches at lists.re-wrenches.org [52]

Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[53]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[54]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[55]

List rules ">  Chris Schaefer [58] May 4, 2021 at 1:41 PM    Jason,  
A valid concern which is why I always wire them as powered open so if there
is a failure it would transition closed or not open.   Christopher  

   --


Chris Schaefer's
Tel/Fax 585-229-2083 or Cell 585-748-1870 
5115 South
Hill Road ~ Canandaigua New York 14424
_www.solarandwindfx.com [60] ~
E-mail: chris at solarandwindfx.com [61]_ 

Thomas Jefferson, the author of
our great Constitution, once said, "democracy" will cease to exist when you
take away from those who are willing to work and give to those who would
not."       

 _______________________________________________
List
sponsored by Redwood Alliance

Pay optional member dues here:
http://re-wrenches.org [62]

List Address:
RE-wrenches at lists.re-wrenches.org [63]

Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[64]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[65]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[66]

List rules ">  Jason Szumlanski [69] May 4, 2021 at 1:03 PM     What
happens when the contactor fails? I don't trust a NC contactor that is
supposed to open on 240Vac coil voltage from the generator. It's not a
failsafe solution.   Jason   


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [70]

List
Address: RE-wrenches at lists.re-wrenches.org [71]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[72]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[73]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[74]

List rules ">  Drake [77] May 4, 2021 at 12:08 PM    P.S. The
contactor method is even mentioned somewhere in the Outback literature.
I've been using it for years. It is very simple and requires no complex
equipment. It will not interfere with rapid shutdown. 40 A, 240 V
contactors with 240 V coils are readily available and not terribly
expensive. The 240 V output of the generator circuit provides the signal.


 At 10:02 AM 5/4/2021, you wrote:


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [78]

List
Address: RE-wrenches at lists.re-wrenches.org [79]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[80]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[81]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[82]

List rules ">  drake.chamberlin at redwoodalliance.org [85] May 4, 2021
at 7:02 AM    Get a contactor with a 240 VAC coil. Connect the coil wire
wires to the 240 V output circuit of the generator, so when the generator
comes on, the contactor opens. Run the current from the AC coupled Enphase
inverters through the contacts from common to N/C.   ---

On 2021-05-03
10:26, Dave Tedeyan wrote: 


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [86]

List
Address: RE-wrenches at lists.re-wrenches.org [87]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[88]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[89]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[90]

List rules ">  Dave Tedeyan [93] May 3, 2021 at 7:26 AM    Hi All, 

I am planning on using a Sol-Ark for the first time for adding battery
backup to an existing system. It is Enphase, so clearly it will be AC
coupled, and there is a whole house generator. When I talked to Sol-Ark
about it, they recommended putting the generator on a time of use schedule
to not allow it to come on during the day so that we don't run into the
issue of the solar backfeeding the generator.   I was wondering though if
anyone has just used a contactor to cut out the solar when the generator
turns on? Something like Outback's GS-AC-Gen-Kit, although in this case I
will need something rated for just over 30A. This seems like a better way
to allow the generator to run at any time it is needed, especially if it is
a gloomy, snowy, winter day.   Cheers,  Dave
   -- 
   DAVE TEDEYAN, PE 

1653 Slaterville Road, Ithaca, NY 14850 Cell: 607-288-2898
www.sungineersolar.com [94]       


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [95]

List
Address: RE-wrenches at lists.re-wrenches.org [96]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[97]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[98]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[99]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
[100]

Check out or update participant
bios:
http://www.members.re-wrenches.org [101]

   

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
mailto:offgridsolar at sti.net
[4] http://members.sti.net/offgridsolar/
[5]
mailto:offgridsolar at sti.net
[6]
mailto:jason at floridasolardesigngroup.com
[7] http://re-wrenches.org
[8]
mailto:RE-wrenches at lists.re-wrenches.org
[9]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[10]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[11]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[12]
http://www.re-wrenches.org/etiquette.htm
[13]
http://www.members.re-wrenches.org
[14]
mailto:jason at floridasolardesigngroup.com
[15] http://re-wrenches.org
[16]
mailto:RE-wrenches at lists.re-wrenches.org
[17]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[18]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[19]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[20]
http://www.re-wrenches.org/etiquette.htm
[21]
http://www.members.re-wrenches.org
[22] mailto:dave at sungineersolar.com
[23]
http://www.sungineersolar.com/
[24] http://re-wrenches.org
[25]
mailto:RE-wrenches at lists.re-wrenches.org
[26]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[27]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[28]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[29]
http://www.re-wrenches.org/etiquette.htm
[30]
http://www.members.re-wrenches.org
[31]
mailto:jerrysgarage01 at gmail.com
[32] http://re-wrenches.org
[33]
mailto:RE-wrenches at lists.re-wrenches.org
[34]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[35]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[36]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[37]
http://www.re-wrenches.org/etiquette.htm
[38]
http://www.members.re-wrenches.org
[39] mailto:offgridsolar at sti.net
[40]
http://members.sti.net/offgridsolar/
[41] mailto:offgridsolar at sti.net
[42]
mailto:dave at sungineersolar.com
[43] http://re-wrenches.org
[44]
mailto:RE-wrenches at lists.re-wrenches.org
[45]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[46]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[47]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[48]
http://www.re-wrenches.org/etiquette.htm
[49]
http://www.members.re-wrenches.org
[50] mailto:dave at sungineersolar.com
[51]
http://re-wrenches.org
[52] mailto:RE-wrenches at lists.re-wrenches.org
[53]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[54]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[55]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[56]
http://www.re-wrenches.org/etiquette.htm
[57]
http://www.members.re-wrenches.org
[58]
mailto:chris at solarandwindfx.com
[59]
http://webmail.sti.net/http:www.solarandwindfx.com
[60]
http://www.solarandwindfx.com
[61] mailto:chris at solarandwindfx.com
[62]
http://re-wrenches.org
[63] mailto:RE-wrenches at lists.re-wrenches.org
[64]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[65]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[66]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[67]
http://www.re-wrenches.org/etiquette.htm
[68]
http://www.members.re-wrenches.org
[69]
mailto:jason at floridasolardesigngroup.com
[70] http://re-wrenches.org
[71]
mailto:RE-wrenches at lists.re-wrenches.org
[72]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[73]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[74]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[75]
http://www.re-wrenches.org/etiquette.htm
[76]
http://www.members.re-wrenches.org
[77]
mailto:drake.chamberlin at redwoodalliance.org
[78]
http://re-wrenches.org
[79] mailto:RE-wrenches at lists.re-wrenches.org
[80]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[81]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[82]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[83]
http://www.re-wrenches.org/etiquette.htm
[84]
http://www.members.re-wrenches.org
[85]
mailto:drake.chamberlin at redwoodalliance.org
[86]
http://re-wrenches.org
[87] mailto:RE-wrenches at lists.re-wrenches.org
[88]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[89]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[90]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[91]
http://www.re-wrenches.org/etiquette.htm
[92]
http://www.members.re-wrenches.org
[93] mailto:dave at sungineersolar.com
[94]
http://www.sungineersolar.com/
[95] http://re-wrenches.org
[96]
mailto:RE-wrenches at lists.re-wrenches.org
[97]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[98]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[99]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[100]
http://www.re-wrenches.org/etiquette.htm
[101]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/ec277aa3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/ec277aa3/attachment.gif>


More information about the RE-Wrenches mailing list