[RE-wrenches] Generator and AC coupling on a Sol-Ark

Dave Tedeyan dave at sungineersolar.com
Fri May 7 11:41:15 EDT 2021


I would certainly agree with you all that AC coupled for off-grid is not
the best design choice. But just for clarification, this is a grid-tied
system where there is already an Enphase M215 system and a whole house
generator set up.
Cheers,
Dave

On Fri, May 7, 2021 at 11:10 AM Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

> I have to agree with Dave on this, complex and off grid generally are not
> good together, l sugest backing up and you might consider a redesign, dump
> enphase, go directly in to the inverter DC side, now a gen set back up will
> work. Your spending more time and effort going in a bad direction. AC
> coupling for resi is not a great solution to start with and Solark even say
> that. KISS is better
> Jerry
> NABCEP PV Inspector
>
> On Thu, May 6, 2021, 7:33 AM Dave Angelini Offgrid Solar <
> offgridsolar at sti.net> wrote:
>
>> I would not do any of this for an offgrid client. It is against the rule
>> of less is more. The whole design is flawed in my opinion.
>>
>>
>>
>> *Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
>> text 209 813 0060*
>>
>> On Tue, 4 May 2021 19:24:13 -0400, Dave Tedeyan <dave at sungineersolar.com>
>> wrote:
>>
>> I suppose the question here is - which is the worse failure mode?
>> A. Solar turning off until an electrician can fix it.
>> OR
>> B. Not knowing the contactor failed until it does not open when the
>> generator turns on and running the risk that the solar backfeeds the
>> generator and breaks it.
>>
>> For off-grid maybe A would be more of a concern. But for grid tied, I
>> would think option B would be worse.
>>
>> Does anyone have a fail safe method of doing this?
>>
>> Cheers,
>> Dave
>>
>> On Tue, May 4, 2021, 4:41 PM Chris Schaefer <chris at solarandwindfx.com>
>> wrote:
>>
>>> Jason,
>>>
>>> A valid concern which is why I always wire them as powered open so if
>>> there is a failure it would transition closed or not open.
>>>
>>> Christopher
>>>
>>> On Tue, May 4, 2021 at 4:15 PM Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>>> What happens when the contactor fails? I don't trust a NC contactor
>>>> that is supposed to open on 240Vac coil voltage from the generator. It's
>>>> not a failsafe solution.
>>>>
>>>> Jason
>>>>
>>>>
>>>>
>>>> On Tue, May 4, 2021, 3:15 PM Drake <
>>>> drake.chamberlin at redwoodalliance.org> wrote:
>>>>
>>>>> P.S. The contactor method is even mentioned somewhere in the Outback
>>>>> literature. I've been using it for years. It is very simple and requires no
>>>>> complex equipment. It will not interfere with rapid shutdown. 40 A, 240 V
>>>>> contactors with 240 V coils are readily available and not terribly
>>>>> expensive. The 240 V output of the generator circuit provides the signal.
>>>>>
>>>>> At 10:02 AM 5/4/2021, you wrote:
>>>>>
>>>>> Get a contactor with a 240 VAC coil. Connect the coil wire wires to
>>>>> the 240 V output circuit of the generator, so when the generator comes on,
>>>>> the contactor opens. Run the current from the AC coupled Enphase inverters
>>>>> through the contacts from common to N/C.
>>>>>
>>>>> ---
>>>>>
>>>>>
>>>>>
>>>>> On 2021-05-03 10:26, Dave Tedeyan wrote:
>>>>>
>>>>> Hi All,
>>>>>
>>>>> I am planning on using a Sol-Ark for the first time for adding battery
>>>>> backup to an existing system. It is Enphase, so clearly it will be AC
>>>>> coupled, and there is a whole house generator. When I talked to Sol-Ark
>>>>> about it, they recommended putting the generator on a time of use schedule
>>>>> to not allow it to come on during the day so that we don't run into the
>>>>> issue of the solar backfeeding the generator.
>>>>>
>>>>> I was wondering though if anyone has just used a contactor to cut out
>>>>> the solar when the generator turns on? Something like Outback's
>>>>> GS-AC-Gen-Kit, although in this case I will need something rated for just
>>>>> over 30A. This seems like a better way to allow the generator to run at any
>>>>> time it is needed, especially if it is a gloomy, snowy, winter day.
>>>>>
>>>>> Cheers,
>>>>> Dave
>>>>>
>>>>> --
>>>>>
>>>>> *Dave Tedeyan, PE * [image: Sungineer Solar]
>>>>> 1653 Slaterville Road, Ithaca, NY 14850
>>>>> Cell: 607-288-2898
>>>>> www.sungineersolar.com
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>
>>>
>>> --
>>>
>>> Chris Schaefer's
>>> <http:www.solarandwindfx.com>
>>>
>>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>>> <http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
>>> <chris at solarandwindfx.com>*
>>>
>>>
>>> Thomas Jefferson, the author of our great Constitution, once said,
>>> "democracy" will cease to exist when you take away from those who are
>>> willing to work and give to those who would not."
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
*Dave Tedeyan, PE*
[image: Sungineer Solar]
1653 Slaterville Road, Ithaca, NY 14850
Cell: 607-288-2898
www.sungineersolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/87c4aa7f/attachment.htm>


More information about the RE-Wrenches mailing list