I have to agree with Dave on this, complex and off grid generally are not
good together, l sugest backing up and you might consider a redesign, dump
enphase, go directly in to the inverter DC side, now a gen set back up will
work. Your spending more time and effort going in a bad direction. AC
coupling for resi is not a great solution to start with and Solark even say
that. KISS is better
Jerry
NABCEP PV Inspector

On Thu, May 6, 2021, 7:33 AM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:

> I would not do any of this for an offgrid client. It is against the rule
> of less is more. The whole design is flawed in my opinion.
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Tue, 4 May 2021 19:24:13 -0400, Dave Tedeyan <dave at sungineersolar.com>
> wrote:
>
> I suppose the question here is - which is the worse failure mode?
> A. Solar turning off until an electrician can fix it.
> OR
> B. Not knowing the contactor failed until it does not open when the
> generator turns on and running the risk that the solar backfeeds the
> generator and breaks it.
>
> For off-grid maybe A would be more of a concern. But for grid tied, I
> would think option B would be worse.
>
> Does anyone have a fail safe method of doing this?
>
> Cheers,
> Dave
>
> On Tue, May 4, 2021, 4:41 PM Chris Schaefer <chris at solarandwindfx.com>
> wrote:
>
>> Jason,
>>
>> A valid concern which is why I always wire them as powered open so if
>> there is a failure it would transition closed or not open.
>>
>> Christopher
>>
>> On Tue, May 4, 2021 at 4:15 PM Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>> What happens when the contactor fails? I don't trust a NC contactor that
>>> is supposed to open on 240Vac coil voltage from the generator. It's not a
>>> failsafe solution.
>>>
>>> Jason
>>>
>>>
>>>
>>> On Tue, May 4, 2021, 3:15 PM Drake <drake.chamberlin at redwoodalliance.org>
>>> wrote:
>>>
>>>> P.S. The contactor method is even mentioned somewhere in the Outback
>>>> literature. I've been using it for years. It is very simple and requires no
>>>> complex equipment. It will not interfere with rapid shutdown. 40 A, 240 V
>>>> contactors with 240 V coils are readily available and not terribly
>>>> expensive. The 240 V output of the generator circuit provides the signal.
>>>>
>>>> At 10:02 AM 5/4/2021, you wrote:
>>>>
>>>> Get a contactor with a 240 VAC coil. Connect the coil wire wires to the
>>>> 240 V output circuit of the generator, so when the generator comes on, the
>>>> contactor opens. Run the current from the AC coupled Enphase inverters
>>>> through the contacts from common to N/C.
>>>>
>>>> ---
>>>>
>>>>
>>>>
>>>> On 2021-05-03 10:26, Dave Tedeyan wrote:
>>>>
>>>> Hi All,
>>>>
>>>> I am planning on using a Sol-Ark for the first time for adding battery
>>>> backup to an existing system. It is Enphase, so clearly it will be AC
>>>> coupled, and there is a whole house generator. When I talked to Sol-Ark
>>>> about it, they recommended putting the generator on a time of use schedule
>>>> to not allow it to come on during the day so that we don't run into the
>>>> issue of the solar backfeeding the generator.
>>>>
>>>> I was wondering though if anyone has just used a contactor to cut out
>>>> the solar when the generator turns on? Something like Outback's
>>>> GS-AC-Gen-Kit, although in this case I will need something rated for just
>>>> over 30A. This seems like a better way to allow the generator to run at any
>>>> time it is needed, especially if it is a gloomy, snowy, winter day.
>>>>
>>>> Cheers,
>>>> Dave
>>>>
>>>> --
>>>>
>>>> *Dave Tedeyan, PE * [image: Sungineer Solar]
>>>> 1653 Slaterville Road, Ithaca, NY 14850
>>>> Cell: 607-288-2898
>>>> www.sungineersolar.com
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>
>>
>> --
>>
>> Chris Schaefer's
>> <http:www.solarandwindfx.com>
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>> <http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
>> <chris at solarandwindfx.com>*
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/7f681abe/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/7f681abe/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210507/7f681abe/attachment-0001.gif>


More information about the RE-Wrenches mailing list