No, I would not use a Sol-Ark unless it was redundant, as in two paralleled
for AC output. I agree with you.
That's the other advantage of AC Coupling in a dual Sol-Ark configuration.
If done right the "extra" AC coupled PV can be usable in the event of a
single inverter failure (to an extent). But I don't have enough experience
with it to know for sure if this is a viable option.
Jason
On Thu, Jan 21, 2021, 5:34 PM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> Hi Jason,
>
> The downside of an all-in one, that may be acceptable for grid, is in a
> failure an all-in-one becomes unusable unless there is a spare. Even with
> one it is often a bigger job to deal with. This was my feedback to
> Schneider when they were looking into this 5 years back. I know they made
> the right decision for offgrid.[image: Wink]
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Thu, 21 Jan 2021 16:05:44 -0500, Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>
> It's already built - 6 years old - I didn't do it. The new property owner
> just purchased a very expensive battery bank and wants to protect it,
> understandably, because she had problems with her generator not starting as
> expected when not at the property. It was suggested by the original
> installer to install a load shedding contactor as the manual suggests
> (albeit in an opaque manner). I just can't seem to wrap my head around why
> this is a good idea. The integrated battery protection mode should handle
> this function. A contactor (or series of relays and a contactor) carries
> too much risk of failure that could result in another problem for the owner
> altogether. I understand protecting the battery, but the cure can't be
> worse than the disease. I'm looking for a balanced approach, which I
> believe is to just implement the BPM unless I'm missing some deficiency in
> that strategy.
>
> The system worked great in an AC coupled configuration until the generator
> started becoming unreliable. In Florida I like AC coupling in a scenario
> like this where the most challenging load is in the summer, essentially
> concurrent with peak sunlight (air conditioning). However, I have been
> looking at trying out a Sol-Ark as soon as the opportunity arises with a
> combination of DC and AC coupling. With no separate charge controller
> involved, it becomes much less complicated and you get the best of both
> worlds in theory.
>
> Jason
>
>
>
>
> On Thu, Jan 21, 2021 at 3:36 PM Tump <tump at swnl.net> wrote:
>
>> IF this system has yet to be built I would STRONGLY suggest that AC
>> coupling is NOT considered. IF it is them i would consider HV CC DC
>> coupling.
>> T
>>
>> On Jan 21, 2021, at 3:15 PM, Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>
>> Hi Mac,
>>
>> Yes, I considered using a pilot relay - it makes sense to run it on 120V
>> because relays are readily available. I had the exact same concern - more
>> to fail.
>>
>> In this scenario, the inverter/battery room is remote from the house so
>> there is only one load I can switch easily with a contactor, and that's the
>> whole house load. Otherwise, I would definitely consider switching
>> non-critical loads in a low battery situation.
>>
>> It just seems prudent enough to use the integrated Battery
>> Preservation Mode (BPM), even in this AC coupled system. I considered a
>> small DC array to charge the batteries in a heavily depleted situation, but
>> it's a 60kWh battery so I would need a pretty substantial "backup" array I
>> think. It does not seem like a reasonable solution. I would expect BPM to
>> do it's job and keep the batteries from reaching a state that they are not
>> recovered quite easily.
>>
>> Jason
>>
>>
>> On Thu, Jan 21, 2021 at 2:37 PM Mac Lewis <maclewis1 at gmail.com> wrote:
>>
>>> Hi Jason,
>>>
>>> The only reason to load shed, without using the internal preservation
>>> mode is if you have certain loads you'd like to keep on longer than other
>>> loads that you shed. The various preservation modes can be complex,
>>> especially if you are AC coupled, so you really have to think through your
>>> strategy.
>>>
>>> You can always use a pilot relay, with a coil rating that suits your
>>> needs, and then feed the 100A contactor with that. Unfortunately, its just
>>> one more piece to fail...
>>>
>>> On Thu, Jan 21, 2021 at 12:13 PM Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>>> I just learned from the manufacturer that the mercury displacement
>>>> relay's coil is rated for 43.2 to 52.80V. Obviously, the battery voltage
>>>> can exceed 52.8 pretty significantly. Does the Sunny Island regulate the
>>>> output voltage on this relay to 48V or is the actual battery voltage passed
>>>> through on this terminal?
>>>>
>>>> The more I read about this load shedding strategy, the more it seems
>>>> overly complicated. It's also another thing to fail. If the N.O. contactor
>>>> coil fails, the loads to the house are going to lose power. That's not good
>>>> for a remote installation. I guess you have to weigh battery protection
>>>> with how critical the loads are.
>>>>
>>>> I'm wondering why the internal Battery Preservation Mode isn't
>>>> sufficient enough. What's the purpose of load shedding if the BPM does
>>>> effectively the same thing. I can see perhaps shedding some parts of the
>>>> load and that is a nice feature, but to protect the batteries, why isn't
>>>> BPM enough?
>>>>
>>>> Jason
>>>>
>>>>
>>>>
>>>> On Tue, Jan 19, 2021 at 8:48 PM Mac Lewis <maclewis1 at gmail.com> wrote:
>>>>
>>>>> Hi Jason,
>>>>>
>>>>> I have done this with mercury displacement relays:
>>>>>
>>>>> https://www.mdius.com/mercury-relays/two-pole-relays-contactors/two-pole-100-amp
>>>>> <https://mailtrack.io/trace/link/d70ece28567af41275941f7d3b22f54c0587b1e3?url=https%3A%2F%2Fwww.mdius.com%2Fmercury-relays%2Ftwo-pole-relays-contactors%2Ftwo-pole-100-amp&userId=1613865&signature=3b642ecb564a461a>
>>>>>
>>>>> They do have a 100A 2P 48V coil relay. They seem to work perfectly.
>>>>>
>>>>> Good luck
>>>>>
>>>>> On Tue, Jan 19, 2021 at 2:51 PM Jason Szumlanski <
>>>>> jason at floridasolardesigngroup.com> wrote:
>>>>>
>>>>>> Does anyone know where I can get a load shedding contactor described
>>>>>> in SMA documentation for use with a multi-function relay in a Sunny Island?
>>>>>>
>>>>>> Thanks,
>>>>>>
>>>>>> Jason Szumlanski
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/caf14456cb57eca504c4e65dd95645c6d312160d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e1c235b1977d450d>
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> <https://mailtrack.io/trace/link/b8e12996216abce9b058ecb74cb725fefd8ade00?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=7f2055d19a086b38>
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/b58558e6db5b64c40668a41b18fde93eab21dbf8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=949757650aaac13b>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/1bb13c515081cd30bc10084f2d4bf11117fe8961?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e82928911a0e2384>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/be9b8d73398559b8311f720a16b3278f3329a93d?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f41b8da35e5653d2>
>>>>>>
>>>>>
>>>>>
>>>>> --
>>>>>
>>>>>
>>>>>
>>>>> Mac Lewis
>>>>>
>>>>> "Yo solo sé que no sé nada." -Sócrates
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/647fed298fee8baf5538b0c39f05944c5f41cf53?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c0a520c8a6ddfd28>
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> <https://mailtrack.io/trace/link/1ccf25fb0e3a2e6b989432e43e9f5ad5ac9e1e54?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=648656cf0c55d1ac>
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/d6b6af87b7ac5c2028222472808d19f96354de51?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6355520506265b13>
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> <https://mailtrack.io/trace/link/9cd2021f46c2f6462d5a73e2bd5711869978f31b?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=3bf244071665a351>
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/d8a58778da4cc375c748c4462173c943ea945778?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f3703ec1bf30fb3f>
>>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/b59d7fd263e25708f25fdde6cfe35432d7c3cc06?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=495a3020266556fc>
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> <https://mailtrack.io/trace/link/cd7fb3f82e59e0bfe82ab4c5badaa037384c9b39?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=2d45e8c05c4bf6fb>
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/c74feeb6aeb0ea52213946ce278f09ffadb8dcda?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=1fc6b5b2f792e92d>
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/557de106b8631de8f8ef389a24fd53963b801008?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=824c950c1562715c>
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/e8ca072330e17f94b4e127840a7c1dc99f4d139a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f9f57f999a5304f4>
>>>>
>>>
>>>
>>> --
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>> "Yo solo sé que no sé nada." -Sócrates
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/96457d1e73955a974bcc93df1bb8f3df6988dc45?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=db610d63dcd7cfa5>
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> <https://mailtrack.io/trace/link/d94ee29d8fb5d7cc21524d9d3645daa1c3db5b8a?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=073a25e08331a861>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/db4d6566601e98a9943b762800a09514ed4f48eb?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b99e12ac3757d8aa>
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/612be3dcf1fe3a2078f5094c71c3627bbce0f5a0?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=75448785f92bc8c9>
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/b3dcc9d84e27b3779b1dc9b22b6843ebab7a122a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=c94498332c695bb0>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/0096685eabcb188c25062b60651f5a77e440b57f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=651e167d30677338>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/52d7126c1474434bdf918e341b49a07e4cfeeeb2?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=63489053658e6470>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/71cb6bc029a54c83700324d4f654692fdad41f08?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=46b473149765c489>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/be1c189911863829f0bbecbc42838e204e1fa440?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e5d5ce425e76c159>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/cbf11d78de365412327ea48783d51143cc38110e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=aca4ae6976db84f3>
>>
>>
>> *Tump at swnl.net* *www.SWNL.net*
>> Solarwinds Northernlights
>> * Serving Mid Coast Maine & Northern California*
>> * 207-832-7574 Cl.
>> 610-517-8401 *
>> *Blair "TUMP" May*
>>
>>
>> * ******** MAINE'S CHARTER ******** * *
>> NABCEP "Certified PV Installer"*
>>
>>
>> * ******** MAINE'S CHARTER ******** **
>> Trace Xantrex "Certified" Dealer / Installer"*
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/f80a0fb3c47ea355610dab14fb3b3c89de7af7ff?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5e3da3d93db52a9a>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/328a39e14759ee3278262dcda048d0a4a4f7ced6?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=5bf63123c2f08f22>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/123e7235a20f09abcb86f5e468fdc3de7dfcb666?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fcf50b166c98dc17>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/431ac2661043e69f876d1e80f1d0abb0b9a00957?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=762a18e51b2ec84d>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/031c631d3d843d96f56ec6a51714a2b3d660488e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5ab4d2d5f1e4294e>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210121/e0f54909/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smiley-wink.gif
Type: image/gif
Size: 350 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210121/e0f54909/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smiley-wink.gif
Type: image/gif
Size: 350 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210121/e0f54909/attachment-0001.gif>
More information about the RE-Wrenches
mailing list