[RE-wrenches] SMA Load Shedding Contactor 100A, 2P

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Fri Jan 22 15:24:38 EST 2021


Use series resistors around the coil. 

---

On 2021-01-21 13:59, Jason Szumlanski wrote:

> I just learned from the manufacturer that the mercury displacement relay's coil is rated for 43.2 to 52.80V. Obviously, the battery voltage can exceed 52.8 pretty significantly. Does the Sunny Island regulate the output voltage on this relay to 48V or is the actual battery voltage passed through on this terminal? 
> 
> The more I read about this load shedding strategy, the more it seems overly complicated. It's also another thing to fail. If the N.O. contactor coil fails, the loads to the house are going to lose power. That's not good for a remote installation. I guess you have to weigh battery protection with how critical the loads are. 
> 
> I'm wondering why the internal Battery Preservation Mode isn't sufficient enough. What's the purpose of load shedding if the BPM does effectively the same thing. I can see perhaps shedding some parts of the load and that is a nice feature, but to protect the batteries, why isn't BPM enough? 
> 
> Jason 
> 
> On Tue, Jan 19, 2021 at 8:48 PM Mac Lewis <maclewis1 at gmail.com> wrote: 
> Hi Jason, 
> 
> I have done this with mercury displacement relays: 
> https://www.mdius.com/mercury-relays/two-pole-relays-contactors/two-pole-100-amp [1] 
> 
> They do have a 100A 2P 48V coil relay.  They seem to work perfectly. 
> 
> Good luck 
> 
> On Tue, Jan 19, 2021 at 2:51 PM Jason Szumlanski <jason at floridasolardesigngroup.com> wrote: 
> Does anyone know where I can get a load shedding contactor described in SMA documentation for use with a multi-function relay in a Sunny Island? 
> 
> Thanks, 
> 
> Jason Szumlanski  _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [2]
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ [3]
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [4]
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm [5]
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [6]
> 
> -- 
> 
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [7]
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ [8]
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [9]
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm [10]
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [11]

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 

Links:
------
[1]
https://mailtrack.io/trace/link/507c3cd242097f112c86a155d1e20d50857a422b?url=https%3A%2F%2Fwww.mdius.com%2Fmercury-relays%2Ftwo-pole-relays-contactors%2Ftwo-pole-100-amp&amp;userId=1613865&amp;signature=1f785f791758ce12
[2]
https://mailtrack.io/trace/link/17da3db56895ddc360fdc714312bb15c810b3d9c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&amp;userId=1613865&amp;signature=c48369ecaf4e553d
[3]
https://mailtrack.io/trace/link/194df01af7007a27cee95e424186cee92dfb90aa?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&amp;userId=1613865&amp;signature=b359cf98f4845669
[4]
https://mailtrack.io/trace/link/a90c679cc6b08e0d8f9d077b1a0286cf0ac4450b?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&amp;userId=1613865&amp;signature=c436e3437bcfefb9
[5]
https://mailtrack.io/trace/link/6cad44ddc698382911f831e8f1c1dac0a8bcc288?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&amp;userId=1613865&amp;signature=4f7688074d106a23
[6]
https://mailtrack.io/trace/link/46eb9172fba39b9b7cf250fe1773ec71c148de8a?url=http%3A%2F%2Fwww.members.re-wrenches.org&amp;userId=1613865&amp;signature=a916ce63ec434074
[7]
https://mailtrack.io/trace/link/709f6cb68c9bbc03071cb9842f0296828f708159?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&amp;userId=1613865&amp;signature=fbe2717c33dde0b9
[8]
https://mailtrack.io/trace/link/f2fb60bbff6e61e6d195e34d56d723dd6f26ad63?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&amp;userId=1613865&amp;signature=f68a2f06bcc591b8
[9]
https://mailtrack.io/trace/link/3147a7eacfc37ebda032d9848afdc4f2325e2fd7?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&amp;userId=1613865&amp;signature=0be6d941cf767375
[10]
https://mailtrack.io/trace/link/70fcc571777b9499feea16489030706bbcdc3569?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&amp;userId=1613865&amp;signature=3e11754cd74c5658
[11]
https://mailtrack.io/trace/link/b701fd0e223b4ee024479d318e2335d0e5f7ad0a?url=http%3A%2F%2Fwww.members.re-wrenches.org&amp;userId=1613865&amp;signature=566dc63b61cef07d
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210122/9628d966/attachment.htm>


More information about the RE-Wrenches mailing list