<div dir="auto">No, I would not use a Sol-Ark unless it was redundant, as in two paralleled for AC output. I agree with you. <div dir="auto"><br></div><div dir="auto">That's the other advantage of AC Coupling in a dual Sol-Ark configuration. If done right the "extra" AC coupled PV can be usable in the event of a single inverter failure (to an extent). But I don't have enough experience with it to know for sure if this is a viable option.</div><div dir="auto"><br></div><div dir="auto">Jason</div><div dir="auto"><br><div dir="auto"><br></div><div dir="auto"><br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Jan 21, 2021, 5:34 PM Dave Angelini Offgrid Solar <<a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><p>Hi Jason,</p>
<p>The downside of an all-in one, that may be acceptable for grid, is in a failure an all-in-one becomes unusable unless there is a spare. Even with one it is often a bigger job to deal with. This was my feedback to Schneider when they were looking into this 5 years back. I know they made the right decision for offgrid.<img title="Wink" src="cid:smiley-wink.gif@sti.net" alt="Wink" border="0"></p>
<div>
<pre> </pre>
<pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" rel="noreferrer">http://members.sti.net/offgridsolar/</a>
e-mail <a href="mailto:offgridsolar@sti.net" target="_blank" rel="noreferrer">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
</div>
<p>On Thu, 21 Jan 2021 16:05:44 -0500, Jason Szumlanski <<a href="mailto:jason@floridasolardesigngroup.com" target="_blank" rel="noreferrer">jason@floridasolardesigngroup.com</a>> wrote:</p>
<blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px;width:100%">
<div dir="ltr">
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif"> </div>
<div dir="ltr">
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif">It's already built - 6 years old - I didn't do it. The new property owner just purchased a very expensive battery bank and wants to protect it, understandably, because she had problems with her generator not starting as expected when not at the property. It was suggested by the original installer to install a load shedding contactor as the manual suggests (albeit in an opaque manner). I just can't seem to wrap my head around why this is a good idea. The integrated battery protection mode should handle this function. A contactor (or series of relays and a contactor) carries too much risk of failure that could result in another problem for the owner altogether. I understand protecting the battery, but the cure can't be worse than the disease. I'm looking for a balanced approach, which I believe is to just implement the BPM unless I'm missing some deficiency in that strategy.</div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif"> </div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif">The system worked great in an AC coupled configuration until the generator started becoming unreliable. In Florida I like AC coupling in a scenario like this where the most challenging load is in the summer, essentially concurrent with peak sunlight (air conditioning). However, I have been looking at trying out a Sol-Ark as soon as the opportunity arises with a combination of DC and AC coupling. With no separate charge controller involved, it becomes much less complicated and you get the best of both worlds in theory.</div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif"> </div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Jason</div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif"> </div>
<div class="gmail_default" style="font-family:arial,helvetica,sans-serif"> </div>
<div>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div style="text-align:center"> </div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">On Thu, Jan 21, 2021 at 3:36 PM Tump <<a href="mailto:tump@swnl.net" target="_blank" rel="noreferrer">tump@swnl.net</a>> wrote:</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid #cccccc;padding-left:1ex">
<div>IF this system has yet to be built I would STRONGLY suggest that AC coupling is NOT considered. IF it is them i would consider HV CC DC coupling.
<div>T<br>
<div>
<blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px;width:100%">
<div>On Jan 21, 2021, at 3:15 PM, Jason Szumlanski <<a href="mailto:jason@floridasolardesigngroup.com" target="_blank" rel="noreferrer">jason@floridasolardesigngroup.com</a>> wrote:</div>
<br>
<div>
<div dir="ltr">
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div dir="ltr">
<div style="font-family:arial,helvetica,sans-serif">Hi Mac,</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">Yes, I considered using a pilot relay - it makes sense to run it on 120V because relays are readily available. I had the exact same concern - more to fail. </div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">In this scenario, the inverter/battery room is remote from the house so there is only one load I can switch easily with a contactor, and that's the whole house load. Otherwise, I would definitely consider switching non-critical loads in a low battery situation. </div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">It just seems prudent enough to use the integrated Battery Preservation Mode (BPM), even in this AC coupled system. I considered a small DC array to charge the batteries in a heavily depleted situation, but it's a 60kWh battery so I would need a pretty substantial "backup" array I think. It does not seem like a reasonable solution. I would expect BPM to do it's job and keep the batteries from reaching a state that they are not recovered quite easily.</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">Jason</div>
<div>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div style="text-align:center"> </div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">On Thu, Jan 21, 2021 at 2:37 PM Mac Lewis <<a href="mailto:maclewis1@gmail.com" target="_blank" rel="noreferrer">maclewis1@gmail.com</a>> wrote:</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid #cccccc;padding-left:1ex">
<div dir="ltr">Hi Jason,
<div> </div>
<div>The only reason to load shed, without using the internal preservation mode is if you have certain loads you'd like to keep on longer than other loads that you shed. The various preservation modes can be complex, especially if you are AC coupled, so you really have to think through your strategy.</div>
<div> </div>
<div>You can always use a pilot relay, with a coil rating that suits your needs, and then feed the 100A contactor with that. Unfortunately, its just one more piece to fail...</div>
</div>
<br>
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">On Thu, Jan 21, 2021 at 12:13 PM Jason Szumlanski <<a href="mailto:jason@floridasolardesigngroup.com" target="_blank" rel="noreferrer">jason@floridasolardesigngroup.com</a>> wrote:</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid #cccccc;padding-left:1ex">
<div dir="ltr">
<div dir="ltr">
<div style="font-family:arial,helvetica,sans-serif">I just learned from the manufacturer that the mercury displacement relay's coil is rated for 43.2 to 52.80V. Obviously, the battery voltage can exceed 52.8 pretty significantly. Does the Sunny Island regulate the output voltage on this relay to 48V or is the actual battery voltage passed through on this terminal?</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">The more I read about this load shedding strategy, the more it seems overly complicated. It's also another thing to fail. If the N.O. contactor coil fails, the loads to the house are going to lose power. That's not good for a remote installation. I guess you have to weigh battery protection with how critical the loads are.</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">I'm wondering why the internal Battery Preservation Mode isn't sufficient enough. What's the purpose of load shedding if the BPM does effectively the same thing. I can see perhaps shedding some parts of the load and that is a nice feature, but to protect the batteries, why isn't BPM enough?</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div style="font-family:arial,helvetica,sans-serif">Jason</div>
<div style="font-family:arial,helvetica,sans-serif"> </div>
<div>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div style="text-align:center"> </div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">On Tue, Jan 19, 2021 at 8:48 PM Mac Lewis <<a href="mailto:maclewis1@gmail.com" target="_blank" rel="noreferrer">maclewis1@gmail.com</a>> wrote:</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid #cccccc;padding-left:1ex">
<div dir="ltr">Hi Jason,
<div> </div>
<div>I have done this with mercury displacement relays:</div>
<div><a href="https://mailtrack.io/trace/link/d70ece28567af41275941f7d3b22f54c0587b1e3?url=https%3A%2F%2Fwww.mdius.com%2Fmercury-relays%2Ftwo-pole-relays-contactors%2Ftwo-pole-100-amp&userId=1613865&signature=3b642ecb564a461a" target="_blank" rel="noreferrer">https://www.mdius.com/mercury-relays/two-pole-relays-contactors/two-pole-100-amp</a></div>
<div> </div>
<div>They do have a 100A 2P 48V coil relay. They seem to work perfectly.</div>
<div> </div>
<div>Good luck</div>
</div>
<br>
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">On Tue, Jan 19, 2021 at 2:51 PM Jason Szumlanski <<a href="mailto:jason@floridasolardesigngroup.com" target="_blank" rel="noreferrer">jason@floridasolardesigngroup.com</a>> wrote:</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid #cccccc;padding-left:1ex">
<div dir="auto">Does anyone know where I can get a load shedding contactor described in SMA documentation for use with a multi-function relay in a Sunny Island?
<div dir="auto"> </div>
<div dir="auto">Thanks,</div>
<div dir="auto"> </div>
<div dir="auto">Jason Szumlanski </div>
</div>
_______________________________________________<br> List sponsored by Redwood Alliance<br> <br> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br> <br> Change listserver email address & settings:<br> <a href="https://mailtrack.io/trace/link/caf14456cb57eca504c4e65dd95645c6d312160d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e1c235b1977d450d" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br> <br> There are two list archives for searching. When one doesn't work, try the other:<br> <a href="https://mailtrack.io/trace/link/b8e12996216abce9b058ecb74cb725fefd8ade00?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=7f2055d19a086b38" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br> <a href="https://mailtrack.io/trace/link/b58558e6db5b64c40668a41b18fde93eab21dbf8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=949757650aaac13b" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br> <br> List rules & etiquette:<br> <a href="https://mailtrack.io/trace/link/1bb13c515081cd30bc10084f2d4bf11117fe8961?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e82928911a0e2384" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br> <br> Check out or update participant bios:<br> <a href="https://mailtrack.io/trace/link/be9b8d73398559b8311f720a16b3278f3329a93d?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f41b8da35e5653d2" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br> </blockquote>
</div>
<br clear="all">
<div> </div>
-- <br>
<div dir="ltr">
<div> </div>
<div><span style="color:#305a78;font-family:'times new roman',serif"> </span></div>
<div> </div>
Mac Lewis<br><br>
<p align="left"><span style="font-family:Verdana,Arial,Helvetica,sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:#305a78"><span style="font-family:'times new roman',serif">"Yo solo sé que no sé nada." </span><span style="font-weight:bold;color:#686868"><span style="font-family:'times new roman',serif">-Sócrates</span></span></span></span></span></p>
</div>
_______________________________________________<br> List sponsored by Redwood Alliance<br> <br> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br> <br> Change listserver email address & settings:<br> <a href="https://mailtrack.io/trace/link/647fed298fee8baf5538b0c39f05944c5f41cf53?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c0a520c8a6ddfd28" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br> <br> There are two list archives for searching. When one doesn't work, try the other:<br> <a href="https://mailtrack.io/trace/link/1ccf25fb0e3a2e6b989432e43e9f5ad5ac9e1e54?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=648656cf0c55d1ac" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br> <a href="https://mailtrack.io/trace/link/d6b6af87b7ac5c2028222472808d19f96354de51?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6355520506265b13" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br> <br> List rules & etiquette:<br> <a href="https://mailtrack.io/trace/link/9cd2021f46c2f6462d5a73e2bd5711869978f31b?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=3bf244071665a351" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br> <br> Check out or update participant bios:<br> <a href="https://mailtrack.io/trace/link/d8a58778da4cc375c748c4462173c943ea945778?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f3703ec1bf30fb3f" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br> </blockquote>
</div>
<img style="display:flex" alt="" width="0" height="0"></div>
_______________________________________________<br> List sponsored by Redwood Alliance<br> <br> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br> <br> Change listserver email address & settings:<br> <a href="https://mailtrack.io/trace/link/b59d7fd263e25708f25fdde6cfe35432d7c3cc06?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=495a3020266556fc" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br> <br> There are two list archives for searching. When one doesn't work, try the other:<br> <a href="https://mailtrack.io/trace/link/cd7fb3f82e59e0bfe82ab4c5badaa037384c9b39?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=2d45e8c05c4bf6fb" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br> <a href="https://mailtrack.io/trace/link/c74feeb6aeb0ea52213946ce278f09ffadb8dcda?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=1fc6b5b2f792e92d" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br> <br> List rules & etiquette:<br> <a href="https://mailtrack.io/trace/link/557de106b8631de8f8ef389a24fd53963b801008?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=824c950c1562715c" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br> <br> Check out or update participant bios:<br> <a href="https://mailtrack.io/trace/link/e8ca072330e17f94b4e127840a7c1dc99f4d139a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f9f57f999a5304f4" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br> </blockquote>
</div>
<br clear="all">
<div> </div>
-- <br>
<div dir="ltr">
<div> </div>
<div><span style="color:#305a78;font-family:'times new roman',serif"> </span></div>
<div> </div>
Mac Lewis<br><br>
<p align="left"><span style="font-family:Verdana,Arial,Helvetica,sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:#305a78"><span style="font-family:'times new roman',serif">"Yo solo sé que no sé nada." </span><span style="font-weight:bold;color:#686868"><span style="font-family:'times new roman',serif">-Sócrates</span></span></span></span></span></p>
</div>
_______________________________________________<br> List sponsored by Redwood Alliance<br> <br> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br> <br> Change listserver email address & settings:<br> <a href="https://mailtrack.io/trace/link/96457d1e73955a974bcc93df1bb8f3df6988dc45?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=db610d63dcd7cfa5" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br> <br> There are two list archives for searching. When one doesn't work, try the other:<br> <a href="https://mailtrack.io/trace/link/d94ee29d8fb5d7cc21524d9d3645daa1c3db5b8a?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=073a25e08331a861" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br> <a href="https://mailtrack.io/trace/link/db4d6566601e98a9943b762800a09514ed4f48eb?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b99e12ac3757d8aa" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br> <br> List rules & etiquette:<br> <a href="https://mailtrack.io/trace/link/612be3dcf1fe3a2078f5094c71c3627bbce0f5a0?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=75448785f92bc8c9" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br> <br> Check out or update participant bios:<br> <a href="https://mailtrack.io/trace/link/b3dcc9d84e27b3779b1dc9b22b6843ebab7a122a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=c94498332c695bb0" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br> </blockquote>
</div>
<img style="display:flex" alt="" width="0" height="0"></div>
_______________________________________________<br>List sponsored by Redwood Alliance<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address & settings:<br><a href="https://mailtrack.io/trace/link/0096685eabcb188c25062b60651f5a77e440b57f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=651e167d30677338" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://mailtrack.io/trace/link/52d7126c1474434bdf918e341b49a07e4cfeeeb2?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=63489053658e6470" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="https://mailtrack.io/trace/link/71cb6bc029a54c83700324d4f654692fdad41f08?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=46b473149765c489" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules & etiquette:<br><a href="https://mailtrack.io/trace/link/be1c189911863829f0bbecbc42838e204e1fa440?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e5d5ce425e76c159" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="https://mailtrack.io/trace/link/cbf11d78de365412327ea48783d51143cc38110e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=aca4ae6976db84f3" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br><br></div>
</blockquote>
</div>
<br>
<div>
<div>
<blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px;width:100%">
<div>
<div>
<div><span><strong><a rel="noreferrer">Tump@swnl.net</a></strong><span style="font:12px Arial"> </span> <a rel="noreferrer"><strong>www.SWNL.net</strong></a></span>
<div>
<div>
<div>
<div style="margin:0px;font:12px"> <span style="font-weight:normal;color:#2d2cfa"> </span><span style="font:18px">Solarwinds Northernlights</span> <strong style="font-weight:normal"><em> </em></strong></div>
<div style="margin:0px;font:10px"><span style="font:12px"><strong><em> Serving Mid Coast Maine & Northern California</em></strong></span><span style="font:10px Arial"><strong><em><br></em></strong></span><strong><em> 207-832-7574 Cl. 610-517-8401 </em></strong></div>
<div style="margin:0px;font:12px"><span style="color:#2d2cfa"><strong><em> </em></strong></span><strong><em>Blair "TUMP" May</em></strong></div>
<p style="margin:5px 0px;font:12px"><span style="color:#000000"><strong><em> ******** MAINE'S CHARTER ********<br> </em></strong></span><strong><em> </em></strong><span style="text-decoration:underline"><strong><em> NABCEP "Certified PV Installer"</em></strong></span><span style="text-decoration:underline;color:#000000"><strong><em> <br></em></strong></span><span style="color:#000000"><strong><em> <br> ******** MAINE'S CHARTER ********<br> </em></strong></span><span style="text-decoration:underline"><strong><em> Trace Xantrex "Certified" Dealer / Installer"</em></strong></span></p>
<div style="margin:0px;font:12px"> </div>
</div>
</div>
</div>
</div>
</div>
</div>
</blockquote>
</div>
</div>
</div>
</div>
_______________________________________________<br> List sponsored by Redwood Alliance<br> <br> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br> <br> Change listserver email address & settings:<br> <a href="https://mailtrack.io/trace/link/f80a0fb3c47ea355610dab14fb3b3c89de7af7ff?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5e3da3d93db52a9a" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br> <br> There are two list archives for searching. When one doesn't work, try the other:<br> <a href="https://mailtrack.io/trace/link/328a39e14759ee3278262dcda048d0a4a4f7ced6?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=5bf63123c2f08f22" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br> <a href="https://mailtrack.io/trace/link/123e7235a20f09abcb86f5e468fdc3de7dfcb666?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fcf50b166c98dc17" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br> <br> List rules & etiquette:<br> <a href="https://mailtrack.io/trace/link/431ac2661043e69f876d1e80f1d0abb0b9a00957?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=762a18e51b2ec84d" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br> <br> Check out or update participant bios:<br> <a href="https://mailtrack.io/trace/link/031c631d3d843d96f56ec6a51714a2b3d660488e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5ab4d2d5f1e4294e" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a><br> </blockquote>
</div>
<img style="display:flex" src="https://webmail.sti.net/tuxedo/program/blocked.gif" alt="" width="0" height="0"></div>
</blockquote>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>