Might want to look at the hub and data cables to the inverters, bad or poor
connections can effect phases of the inverters, l have seen this manifest
it self with errors like inverter firmware issues  that in fact are bogus.
The OEM cat 5 cables are not shielded and that causes problem when they are
wrapped all around in a box. Easy to test with meters, how many times have
you just rebooted or unplugged something for it all to get better.
Anyway thats just one of many great ideas
Jerry
 NABCEP Inspector
NABCEP Installer

On Fri, Dec 11, 2020, 6:01 PM Jon Siegenthaler <jon.siegenthaler at gmail.com>
wrote:

> Hey wrenches,
>
> I have a client who has a couple of the Radian 8048's and has an error
> code of "AC Backfeed Error GS-1". Looking at the manual it states that
> "Usually indicates another AC power source (out of phase with the inverter)
> was connected to the unit’s AC output. Can also occur if an out-of-phase AC
> source is connected to the inverter’s AC input."
>
> However when this happened the generator wasn't running and it's an off
> grid system. Is there a way that the master is looking to the slave as
> another power source? The system had been running fine this week, auto
> running the generator early morning and shutting down on its own.
>
> Anyone seen something like this before? Thanks,
>
> Jon Siegenthaler
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201211/ace8c0d8/attachment.htm>


More information about the RE-Wrenches mailing list