[RE-wrenches] Outback AC Backfeed Error
Barton Churchill
bchurchill at energy-1.net
Fri Dec 11 23:12:49 EST 2020
You could try going through the stacking sequence again to make sure they can synchronize properly. This is a good test of that output relay in each Radian. If there's a problem, you won't hear them, and they are noisy. Like the instructions state be sure the output breakers are open!
[cid:699e3bd7-2852-4ad0-830e-dc63c6fa2b82]Barton Churchill
Director, Power Division
2042 Stadium Drive Suite 2 • Bozeman, MT 59715 • (O) 406-587-2917 • (D) 406-589-4493
235 E. Broadway • Jackson, WY 83001 • (O) 307-200-2210
bchurchill at energy-1.net<mailto:blansing at energy-1.net> | www.energy-1.net<http://www.energy-1.net/>
________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Chris Worcester <chris at solarwindworks.com>
Sent: Friday, December 11, 2020 7:20 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Outback AC Backfeed Error
Hi Jon,
I have seen this early on, when the Mate3 first came out. The slave back fed the master. The Mate3 didn't accept our programming, a firmware update corrected this glitch.
Chris Worcester
chris at solarwindworks.com
530-448-9692
Sent from my Samsung Galaxy s9.
-------- Original message --------
From: Jon Siegenthaler <jon.siegenthaler at gmail.com>
Date: 12/11/20 6:01 PM (GMT-08:00)
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Outback AC Backfeed Error
Hey wrenches,
I have a client who has a couple of the Radian 8048's and has an error code of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually indicates another AC power source (out of phase with the inverter) was connected to the unit’s AC output. Can also occur if an out-of-phase AC source is connected to the inverter’s AC input."
However when this happened the generator wasn't running and it's an off grid system. Is there a way that the master is looking to the slave as another power source? The system had been running fine this week, auto running the generator early morning and shutting down on its own.
Anyone seen something like this before? Thanks,
Jon Siegenthaler
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201212/28198d6f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-1oslbg0i.png
Type: image/png
Size: 7692 bytes
Desc: Outlook-1oslbg0i.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201212/28198d6f/attachment.png>
More information about the RE-Wrenches
mailing list