[RE-wrenches] Mixing Outback 100 series C with old FX system

Jay jay.peltz at gmail.com
Mon Oct 19 14:55:59 EDT 2020


On page 71 there is a small note about hooking up a FNDC without an inverter. 

It might be what Brad was mentioning. 

Jay 


> On Oct 19, 2020, at 12:48 PM, Dan Fink <danbob88 at gmail.com> wrote:
> 
> 
> Maybe Brad is referring to the GFDI jumper or the RSS jumper? I don't know of a jumper to activate comms with the Mate 3S.
> 
> The former is for bonding and you remove it if you use an external GFDI, like a Midnite GFCI in a Midnite MNDC enclosure. It's the little black wire with 2 red spade connectors under the terminal block. 
> 
> The RSS jumper you have to make out of a scrap of wire to DIS-able the Flexmax 100 internal RSS trigger. It goes between the yellow and purple terminal blocks. If you don't install it, the CC assumes the RSS has been activated. I love this one for my students, when their homework before lab class is to *thoroughly* read the instructions and make notes! I can easily tell if they actually did LOL.
> 
> Dan Fink
> Owner, Buckville Energy Consulting
> NABCEP Certified PV System Inspector
> IREC Certified Instructorâ„¢ for: 
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP Registered Continuing Education Providers
> danbob88 at gmail.com
> 970-672-4342
> 
>  
>> On Sat, Oct 17, 2020 at 8:11 AM Bradley Bassett <bbassett2 at gmail.com> wrote:
>> I think there is a jumper in the FM100 that will allow the Mate3s to communicate with it. I don't remember off hand where it is and am not at a computer with that info, but maybe this will prompt a look at the manual to see if they mention it.
>> 
>> Brad
>> 
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201019/ff78e7e7/attachment.htm>


More information about the RE-Wrenches mailing list