[RE-wrenches] Mixing Outback 100 series C with old FX system

Bradley Bassett bbassett2 at gmail.com
Mon Oct 19 19:35:39 EDT 2020


Jay, thanks yes that is correct, it was a jumper to allow the FNDC to work.
I had no trouble connecting a Mate3s to the FM100-AFCI.

Brad

On Mon, Oct 19, 2020 at 12:37 PM Jay <jay.peltz at gmail.com> wrote:

> On page 71 there is a small note about hooking up a FNDC without an
> inverter.
>
> It might be what Brad was mentioning.
>
> Jay
>
>
> On Oct 19, 2020, at 12:48 PM, Dan Fink <danbob88 at gmail.com> wrote:
>
> 
> Maybe Brad is referring to the GFDI jumper or the RSS jumper? I don't know
> of a jumper to activate comms with the Mate 3S.
>
> The former is for bonding and you remove it if you use an external GFDI,
> like a Midnite GFCI in a Midnite MNDC enclosure. It's the little black wire
> with 2 red spade connectors under the terminal block.
>
> The RSS jumper you have to make out of a scrap of wire to DIS-able the
> Flexmax 100 internal RSS trigger. It goes between the yellow and purple
> terminal blocks. If you don't install it, the CC assumes the RSS has been
> activated. I love this one for my students, when their homework before lab
> class is to *thoroughly* read the instructions and make notes! I can easily
> tell if they actually did LOL.
>
> Dan Fink
> Owner, Buckville Energy Consulting
> NABCEP Certified PV System Inspector
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP Registered Continuing Education Providers
> d <dan.fink at greendustrialtraining.com>anbob88 at gmail.com
> 970-672-4342
>
>
> On Sat, Oct 17, 2020 at 8:11 AM Bradley Bassett <bbassett2 at gmail.com>
> wrote:
>
>> I think there is a jumper in the FM100 that will allow the Mate3s to
>> communicate with it. I don't remember off hand where it is and am not at a
>> computer with that info, but maybe this will prompt a look at the manual to
>> see if they mention it.
>>
>> Brad
>>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201019/7672d12c/attachment.htm>


More information about the RE-Wrenches mailing list