[RE-wrenches] Enphase Envoy Enclosures

Jason Szumlanski jason at floridasolardesigngroup.com
Fri Oct 2 08:41:16 EDT 2020


Answers to your questions/comments:

1. The same voltage in the panelboard would also apply to the junction box
in which it would be located (as suggested by Enphase). You have to bring a
240V 3-wire circuit to the Envoy in its enclosure. I don't see the
difference.
2. Enphase's IQ combiner is only good for 52 IQ7+ micros. These systems are
much larger.
3.Yes. Tested. Successful.
4.There isn't quite *that* much extra room, but ample room for the Envoy on
a DIN rail.
5. I ma hesitant as well. Absent some good answers from Enphase, it's a
tough call because I don't consider their documented solution
compliant given that you can't ground the DIN rail they provide.



<https://mailtrack.io/trace/link/cd7ee5b8f72f9150cba39549b618d038dca6f767?url=http%3A%2F%2Fwww.floridasolardesigngroup.com%2F&userId=1613865&signature=a4cdfea4a151220f>
*Jason Szumlanski*
Principal Solar Designer | Florida Solar Design Group
(239) 491-8010 (239) 410-4985
www.FloridaSolarDesignGroup.com
<https://mailtrack.io/trace/link/c677689c3f678ffaffc928248903416b6527e0d4?url=http%3A%2F%2Fwww.FloridaSolarDesignGroup.com&userId=1613865&signature=51d821586fb66e26>
[image: Facebook]
<https://mailtrack.io/trace/link/f25733ecf11782bdea1c7a9b0b578bbd7b7e645d?url=https%3A%2F%2Fwww.facebook.com%2Ffloridasolardesigngroup&userId=1613865&signature=b9bf743399157a4f>
[image:
Twitter]
<https://mailtrack.io/trace/link/9db60e6983ff51be3465543c64d70f5ac39b5392?url=https%3A%2F%2Ftwitter.com%2FFloridaSolarDG&userId=1613865&signature=f0f6684ccf90f946>
[image:
Youtube]
<https://mailtrack.io/trace/link/7e09bbb712d3ed6735c5bf2febabb0569a23e382?url=https%3A%2F%2Fwww.youtube.com%2Fchannel%2FUCjnsYt5r7DNJD3ZnqI10j8g&userId=1613865&signature=6873b4330fbe90e3>



On Fri, Oct 2, 2020 at 4:07 AM William Miller <william at millersolar.com>
wrote:

> Jason:
>
>
>
> Several issues come to mind:
>
>
>
> 1.   I think the question that dictates is the insulation rating of the
> Envoy and associated wiring as possibly exposed to voltages within the
> panelboard.  This is akin, but not identical, to the scenario described in
> NEC 300.3(C).  Insulation rating matters if any low voltage equipment could
> in any odd-ball scenario contact an energized part.  I don’t imagine the
> Envoy assembly has an insulation rating.  The insulation rating must also
> apply to any communications, CT or any other purposed conductors associated
> the Envoy.  Indeed, this is the same problem regularly encountered when
> installing energy monitor equipment, such as E-gauge or similar, in panels.
>
> 2.   If there are any power line communications interference problems,
> you want your Enphase branch circuits to land in a separate sub-panel so
> you can apply filtering if needed.  The Envoy must be connected to that
> sub-panel.  Enphase makes some custom combiners for this specific purpose.
> Any reason you are not using a sub-panel or Enphase combiner to collect
> Enphase circuits?
>
> 3.   If the Envoy is in a metal can will the Wi-Fi work?
>
> 4.   If there is so much room, would you consider mounting an enclosure
> in the panel inside of which the Envoy could be mounted?  A PVC pull box,
> as one option, would not diminish the Wi-Fi signal any more than it already
> is and would provide the insulation needed to keep energized parts away
> from the low voltage equipment that is the Envoy.  I have even bent up some
> galvanized sheet metal partitions to install in breaker panels.  If well
> fabricated and bonded, this has made me feel warm and fuzzy about the
> safety of same.
>
> 5.   Based on the above, I would not put a naked Envoy in a breaker panel
> unless it was my own house.
>
>
>
> I hope these musings help you decide on a design strategy that you and the
> AHJ think is safe and legal.
>
>
>
> Sincerely,
>
>
>
> William Miller
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
> <https://mailtrack.io/trace/link/5dd283a39fd90538d788acedda94c8e99c05b474?url=http%3A%2F%2Fwww.millersolar.com%2F&userId=1613865&signature=f5aaf0e548f4604a>
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski
> *Sent:* Thursday, October 1, 2020 2:00 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Enphase Envoy Enclosures
>
>
>
> Can anyone point to any code issues with mounting an Envoy inside of a
> panelboard? For example, when installing a 3-phase commercial system with a
> large 400A AC combiner panelboard, there is often PLENTY of room to mount
> an Envoy inside on a DIN rail. Aside from the manufacturer's instructions
> not specifically listing this option, I can't see any reason that it would
> be prohibited. The only downside I can see would be slightly more difficult
> access to service buttons.
>
>
>
> I would argue that it is better. The DIN rail would be bonded to the
> enclosure. The DIN rail that Enphase ships with the Envoy is too short to
> accept a DIN mounted grounding terminal. When mounting in a non-metallic
> enclosure I run an EGC to a grounding terminal on a longer DIN rail that I
> install, not the included one. I'm wondering how people handle the lack of
> a ground terminal on the Envoy and whether they even run an EGC along with
> the circuit conductors when mounting an Envoy in a non-metallic enclosure.
> I have not been able to get a good answer from Enphase on how they expect
> this to be accomplished. I suppose if the Envoy does not need an equipment
> ground because it is insulated, and the DIN rail is not exposed once the
> Envoy is mounted. Maybe it is their opinion that no EGC is required, but I
> see the DIN rail as needing an EGC.
>
>
>
> Anyway, that's a lengthy side note. I'm mainly wondering if the Envoy can
> be mounted in a panelboard.
>
>
>
>
>
>
>
> Jason Szumlanski
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/6004e2c9f3aa5c290f013353a35c2fd14aedb81b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=982167804d1de11d>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/e8f908e284f0c692ed4e3e8cfa8f90407e5217ef?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=d3e09c9e28cb3289>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/fceb12d4143fa2095259475c2b27adc623615ad1?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=81b751c7b05c4f71>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/c726fa22ff2d42404f9f41b0e3207f82c2b64b44?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e8ac6c385feba8de>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201002/de00c3bb/attachment.htm>


More information about the RE-Wrenches mailing list