[RE-wrenches] Microgrid... Outback or SMA or other?

Jason Szumlanski jason at floridasolardesigngroup.com
Thu Sep 10 07:44:36 EDT 2020


There is a huge distinction in a hybrid inverter that integrates MPPT
charge control. Eliminating all of the extraneous hardware and circuit
protection associated with charge controllers is very appealing. The 500V
input limit is also a game-changer in terms of wire size. I'm very
interested in this approach.

On the flip size, an AC Coupled approach is also appealing in a lot of
circumstances. Since Sol-Ark supports that, too, it's hard to find
downsides other than their infancy in the industry.

And for what it's worth, my experience with SMA tech support recently has
been abysmal. Long hold times and getting bounced around departments.

Jason Szumlanski



On Wed, Sep 9, 2020 at 9:50 PM Mark Frye <markf at berkeleysolar.com> wrote:

> The most important thing here is that no one is standing up to sing the
> praises of either SMA or Outback.
>
> I myself have sent about 2 hours on hold over 2 days trying to get an
> issue addressed by SMA.
>
> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
> exchange for good technical support.
> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>
> Any tips on combining AC output from these units when stacking several of
> them? What bus/OCPD system are you using? Same question for generator/grid
> input.
>
> The solar MPPT inputs appear to be dead simple.
>
> Jason Szumlanski
>
>
>
>
>
>
>
>
> On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels <spaceshipnelson1 at gmail.com>
> wrote:
>
>> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with
>> a TON of surge capabilities..
>>
>> Joe Nelson
>>
>> Project Manager C-46/C-10
>> Sustainable Energy Group Inc., A California Corporation
>>
>> CSL# 868816
>> www.SustainableEnergyGroup.com
>> <https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
>> 530-273-4422 (Office)
>>
>> 530-217-8385 (Cell)
>>
>>>>
>>    
>>
>>
>> ------------------------------
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>> behalf of pgiroux at mindspring.com <pgiroux at mindspring.com>
>> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
>> *To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program,
>> does a wonderful job in either ac coupling, stand alone or pure off grid
>> and terrific customer support.
>>
>>
>>
>> Peter Giroux
>>
>> ASAE
>>
>>
>>
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>> Behalf Of *Bryan Norkunas
>> *Sent:* Tuesday, September 8, 2020 1:50 PM
>> *To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>>
>> Sol-Arks would be possible, you can link 8 inverters.
>>
>>
>>
>> *Bryan *
>>
>> *PV-Cables*
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
>> <re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *Chris
>> Schaefer
>> *Sent:* Tuesday, September 8, 2020 10:40 AM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>>
>> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
>> their 12kw unit. Not sure what their max number of inverters are.
>>
>>
>>
>> Christopher
>>
>>
>>
>> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield <maxfieldsolar at hotmail.com>
>> wrote:
>>
>> Hey all, I'm designing a microgrid sized off-grid system for somebody,
>> and I'm just wondering if anyone knows of any issues with the following
>> designs...
>>
>>
>>
>> The client says he needs 70 kW. His load data looks pretty solid, so I'm
>> sticking to using that number as a minimum, at least during the initial
>> proposal stage. I only know of two possible equipment options for this size
>> range...
>>
>>
>>
>>    1. I think I can use up to 10 Outback Radians, for up to an 80 kW
>>    system. Are there any bugs or problems with using this many inverters on
>>    one hub? I know I've read about issues with selling to the grid, but that's
>>    not an issue, this is off-grid.
>>    2. I know that the SMA cluster box with sunny islands can allow for
>>    up to a 72 kW system. Do you know of any bugs or problems with this system?
>>
>>
>>
>>
>>
>> Are there any other options that anyone would suggest? Schneider's
>> website says they can only do up to 61 kW, and Victron can only do up to 60
>> kW.
>>
>>
>>
>>
>>
>> I know that the Outback system would yield a 240/120 Split-Phase system
>> and that the SMA would yield a 208/120 3Ø system, but this doesn't really
>> matter either way for this job.
>>
>>
>>
>> Thanks so much,
>>
>> Kienan
>>
>>
>>
>>
>>
>> *Maxfield Solar*
>>
>> *maxfieldsolar at hotmail.com* <maxfieldsolar at hotmail.com>
>>
>> *(801) 631-5584 (Cell)*
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/7118772550f67326bf449e9f3105d94b2a7b74b4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e1b83eb5e4f926e7>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/c5457950749993eaf94dc7f72a33825e6e66fb1b?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0031eb630b917fa3>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/863e7b45d70c42504299d435c477fd7ce070a999?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=201d4fc86e181859>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/b5c596979aba68fb00e5e571f62bcbaeaadd3618?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b27563b3083d3ceb>
>>
>>
>>
>>
>> --
>>
>> Chris Schaefer’s
>> [image: Image removed by sender.]
>> <https://mailtrack.io/trace/link/6b69a480ea4449f57c42f803d4a726d5ddf0ccc4?url=http%3A%2F%2Fwww.solarandwindfx.com%2F&userId=1613865&signature=6bb84a96dad38d97>
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870  *
>> *5115 South Hill Road ~ Canandaigua New York 14424 www.solarandwindfx.com
>> <https://mailtrack.io/trace/link/864e18304c1425fb0f58d6ed8ea0e16c3e9402d7?url=http%3A%2F%2Fwww.solarandwindfx.com&userId=1613865&signature=87fa9d489354e433>
>> ~ E-mail: **chris at solarandwindfx.com <chris at solarandwindfx.com>*
>>
>> *[image: Image removed by sender.]*
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>>
>>
>> <https://mailtrack.io/trace/link/f4964f47f3632046571a644ebfc74dd37fc349ab?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=7ef512bd066bbd50> Virus-free.
>> www.avg.com
>> <https://mailtrack.io/trace/link/48a44a842703a6744e4bd9b4bdadc457b6f4638e?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=3e478a2a375a7bc5>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/fc1b2521beb6ed5044854d33d56b95e71ca61590?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b85aa44e99dc5faf>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/1b09831c60927375ede751a7f47a27309b4c858c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6712962d0ceaf701>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/de9674746eedb972903621c016fadae65329a20d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=164d7b7638da0383>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/9b916e5e7e182544268c032b7ad89b5bb3ec64ad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bee7ba1ac877929f>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <https://mailtrack.io/trace/link/bc1dfc88c7999f47f10d4f75be24b0b1a9107e47?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=3af4cd2f9e95c66c>
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <https://mailtrack.io/trace/link/8a35d4ef560780fc7340088e0b755a516ee757d8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=14abd03ed82088c4>
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm <https://mailtrack.io/trace/link/1223e546d7c2d1872fa70dc8605af274ff2665de?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ad527ae315c76471>
>
> Check out or update participant bios:www.members.re-wrenches.org <https://mailtrack.io/trace/link/0f9efb827e162f2d58e74b3f0f046a32945e2edb?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=87bd1495e740447a>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/d0deefc4e6a8debd5b8abdde3afc44c86994f28c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=56c8ac84b4211516>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/4de70129f1d6519ae4887f672f558b51a6285743?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=177d5b1c95cbef2c>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/9cb9a72d33ec8e47fe536b23930788f42715d6a5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2f4d3d48fc28f962>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/241a1c2847564fc6df61a1f14b2d66ea535594fe?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=9020190af4c79c8f>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200910/e444d2cd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 425 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200910/e444d2cd/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 463 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200910/e444d2cd/attachment-0001.jpg>


More information about the RE-Wrenches mailing list