[RE-wrenches] Microgrid... Outback or SMA or other?
penobscotsolar at midmaine.com
penobscotsolar at midmaine.com
Thu Sep 10 10:41:03 EDT 2020
We've had great luck using the Tigo (and SMA) optimizers with SolArk to
conform to NEC2017 and CEC2018.
> There is a huge distinction in a hybrid inverter that integrates MPPT
> charge control. Eliminating all of the extraneous hardware and circuit
> protection associated with charge controllers is very appealing. The 500V
> input limit is also a game-changer in terms of wire size. I'm very
> interested in this approach.
>
> On the flip size, an AC Coupled approach is also appealing in a lot of
> circumstances. Since Sol-Ark supports that, too, it's hard to find
> downsides other than their infancy in the industry.
>
> And for what it's worth, my experience with SMA tech support recently has
> been abysmal. Long hold times and getting bounced around departments.
>
> Jason Szumlanski
>
>
>
> On Wed, Sep 9, 2020 at 9:50 PM Mark Frye <markf at berkeleysolar.com> wrote:
>
>> The most important thing here is that no one is standing up to sing the
>> praises of either SMA or Outback.
>>
>> I myself have sent about 2 hours on hold over 2 days trying to get an
>> issue addressed by SMA.
>>
>> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
>> exchange for good technical support.
>> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>>
>> Any tips on combining AC output from these units when stacking several
>> of
>> them? What bus/OCPD system are you using? Same question for
>> generator/grid
>> input.
>>
>> The solar MPPT inputs appear to be dead simple.
>>
>> Jason Szumlanski
>>
>>
>>
>>
>>
>>
>>
>>
>> On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels <spaceshipnelson1 at gmail.com>
>> wrote:
>>
>>> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW,
>>> with
>>> a TON of surge capabilities..
>>>
>>> Joe Nelson
>>>
>>> Project Manager C-46/C-10
>>> Sustainable Energy Group Inc., A California Corporation
>>>
>>> CSL# 868816
>>> www.SustainableEnergyGroup.com
>>> <https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
>>> 530-273-4422 (Office)
>>>
>>> 530-217-8385 (Cell)
>>>
>>> 
>>>
>>>    
>>>
>>>
>>> ------------------------------
>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>>> behalf of pgiroux at mindspring.com <pgiroux at mindspring.com>
>>> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
>>> *To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to
>>> program,
>>> does a wonderful job in either ac coupling, stand alone or pure off
>>> grid
>>> and terrific customer support.
>>>
>>>
>>>
>>> Peter Giroux
>>>
>>> ASAE
>>>
>>>
>>>
>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>>> Behalf Of *Bryan Norkunas
>>> *Sent:* Tuesday, September 8, 2020 1:50 PM
>>> *To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>>
>>> Sol-Arks would be possible, you can link 8 inverters.
>>>
>>>
>>>
>>> *Bryan *
>>>
>>> *PV-Cables*
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *Chris
>>> Schaefer
>>> *Sent:* Tuesday, September 8, 2020 10:40 AM
>>> *To:* RE-wrenches
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>>
>>> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
>>> their 12kw unit. Not sure what their max number of inverters are.
>>>
>>>
>>>
>>> Christopher
>>>
>>>
>>>
>>> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield
>>> <maxfieldsolar at hotmail.com>
>>> wrote:
>>>
>>> Hey all, I'm designing a microgrid sized off-grid system for somebody,
>>> and I'm just wondering if anyone knows of any issues with the following
>>> designs...
>>>
>>>
>>>
>>> The client says he needs 70 kW. His load data looks pretty solid, so
>>> I'm
>>> sticking to using that number as a minimum, at least during the initial
>>> proposal stage. I only know of two possible equipment options for this
>>> size
>>> range...
>>>
>>>
>>>
>>> 1. I think I can use up to 10 Outback Radians, for up to an 80 kW
>>> system. Are there any bugs or problems with using this many
>>> inverters on
>>> one hub? I know I've read about issues with selling to the grid, but
>>> that's
>>> not an issue, this is off-grid.
>>> 2. I know that the SMA cluster box with sunny islands can allow for
>>> up to a 72 kW system. Do you know of any bugs or problems with this
>>> system?
>>>
>>>
>>>
>>>
>>>
>>> Are there any other options that anyone would suggest? Schneider's
>>> website says they can only do up to 61 kW, and Victron can only do up
>>> to 60
>>> kW.
>>>
>>>
>>>
>>>
>>>
>>> I know that the Outback system would yield a 240/120 Split-Phase system
>>> and that the SMA would yield a 208/120 3Ø system, but this doesn't
>>> really
>>> matter either way for this job.
>>>
>>>
>>>
>>> Thanks so much,
>>>
>>> Kienan
>>>
>>>
>>>
>>>
>>>
>>> *Maxfield Solar*
>>>
>>> *maxfieldsolar at hotmail.com* <maxfieldsolar at hotmail.com>
>>>
>>> *(801) 631-5584 (Cell)*
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/7118772550f67326bf449e9f3105d94b2a7b74b4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e1b83eb5e4f926e7>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/c5457950749993eaf94dc7f72a33825e6e66fb1b?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0031eb630b917fa3>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/863e7b45d70c42504299d435c477fd7ce070a999?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=201d4fc86e181859>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/b5c596979aba68fb00e5e571f62bcbaeaadd3618?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b27563b3083d3ceb>
>>>
>>>
>>>
>>>
>>> --
>>>
>>> Chris Schaefer’s
>>> [image: Image removed by sender.]
>>> <https://mailtrack.io/trace/link/6b69a480ea4449f57c42f803d4a726d5ddf0ccc4?url=http%3A%2F%2Fwww.solarandwindfx.com%2F&userId=1613865&signature=6bb84a96dad38d97>
>>>
>>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>>> *5115 South Hill Road ~ Canandaigua New York 14424
>>> www.solarandwindfx.com
>>> <https://mailtrack.io/trace/link/864e18304c1425fb0f58d6ed8ea0e16c3e9402d7?url=http%3A%2F%2Fwww.solarandwindfx.com&userId=1613865&signature=87fa9d489354e433>
>>> ~ E-mail: **chris at solarandwindfx.com <chris at solarandwindfx.com>*
>>>
>>> *[image: Image removed by sender.]*
>>>
>>> Thomas Jefferson, the author of our great Constitution, once said,
>>> "democracy" will cease to exist when you take away from those who are
>>> willing to work and give to those who would not."
>>>
>>>
>>> <https://mailtrack.io/trace/link/f4964f47f3632046571a644ebfc74dd37fc349ab?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=7ef512bd066bbd50>
>>> Virus-free.
>>> www.avg.com
>>> <https://mailtrack.io/trace/link/48a44a842703a6744e4bd9b4bdadc457b6f4638e?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=3e478a2a375a7bc5>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/fc1b2521beb6ed5044854d33d56b95e71ca61590?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b85aa44e99dc5faf>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/1b09831c60927375ede751a7f47a27309b4c858c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6712962d0ceaf701>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/de9674746eedb972903621c016fadae65329a20d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=164d7b7638da0383>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/9b916e5e7e182544268c032b7ad89b5bb3ec64ad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bee7ba1ac877929f>
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address &
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/bc1dfc88c7999f47f10d4f75be24b0b1a9107e47?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=3af4cd2f9e95c66c>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/8a35d4ef560780fc7340088e0b755a516ee757d8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=14abd03ed82088c4>
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/1223e546d7c2d1872fa70dc8605af274ff2665de?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ad527ae315c76471>
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/0f9efb827e162f2d58e74b3f0f046a32945e2edb?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=87bd1495e740447a>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/d0deefc4e6a8debd5b8abdde3afc44c86994f28c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=56c8ac84b4211516>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/4de70129f1d6519ae4887f672f558b51a6285743?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=177d5b1c95cbef2c>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/9cb9a72d33ec8e47fe536b23930788f42715d6a5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2f4d3d48fc28f962>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/241a1c2847564fc6df61a1f14b2d66ea535594fe?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=9020190af4c79c8f>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list