[RE-wrenches] Ampacity Ratings for Different Conductors
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Aug 12 14:16:38 EDT 2020
I use 2/0 mainly because the 4 kw SW and Outback 24v inverters usually
have a 175A or a greater breaker where I go 4/0. This allows the user to
have some flexibility down the line. 24v bat cable loss is a higher issue
also with pump surges. The pre-made cables from AEE ">Dave Angelini Offgrid
Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail offgridsolar at sti.net [2]
text 209 813 0060
On Wed, 12 Aug 2020
11:27:36 -0400, Tump wrote: Seems like over kill and I too am wondering
why use anything but UL listed wire. I always use tinned cable from Cobra.
They have the "X FLEX" and the "X FLEX 150" the X flex #2AWG is good for
213 Amps 2/0 is good for 336 Amps. The X FLEX 150 #2AWG is good for 255 and
the 2/0 is good for 390 Amps. Let me know off list if you wold like my
sales rep, Good quick service. T
On Aug 11, 2020, at 10:34 PM, Glenn
Burt wrote:
Okay I have to ask, why wouldn't you want to stick to code
compliant battery cabling? FROM: RE-wrenches ON BEHALF OF
petertor at pobox.com [5]
SENT: Tuesday, August 11, 2020 6:18 PM
TO:
RE-wrenches at lists.re-wrenches.org [6]
SUBJECT: [RE-wrenches] Ampacity
Ratings for Different Conductors I have been designing a off-grid
system that can fit in an outside-accessible compartment with an
approximate 24" square footprint and space above about 18" - 24". I
am using two Battle Born LiFePO4 batteries rated at 24 V / 50 Ah, a Cotek
pure sine wave inverter with an output power of 4,000 VA , a MorningStar
TS-MPPT-60 charge controller, a Victron BMV-712 "coulomb counter" and a
Battle Born surge limiter CL500. The current limiter limits the
current to 120 continuous, and 200 A for 30 sec. I have been able to
fit everything in and I am designing the cabling, and here is my problem.
I have one vendor that recommends Ancor brand Tinned Marine Grade
Battery Cable. It is "resistant to salt water, battery acid, oil, gasoline,
heat, abrasion and ultra-violet radiation. Exceeds UL 1426, ABYC and US
Coast Guard Charter boat (CFR Title 46) standards. Highest quality
ultra-flexible (Type 3) tinned copper stranding. Vinyl insulation. -50
deg-C to 105 deg-C." 2 AWG is composed of 665 ea 30 AWG stands. The
same vendor has "welding cable" with an EPDM insulation rated at 600 V,
water/chemical/grease/abrasion resistant, -50 deg-C to 105 deg-C, "marine
grade". Not UL listed. 624 ea 30 AWG strands. Roughly comparable
pricing. They claim both 2 AWG cables are rated at 210 A. Not sure
if this is continuous duty or whether I should derate this for what will be
continuous duty. This is new territory for me, and any help would be
appreciated. Peter T. Parrish, Ph.D.
President, California Solar
Engineering _______________________________________________
List
sponsored by Redwood Alliance
List Address:
RE-wrenches at lists.re-wrenches.org [7]
Change listserver email address
font-size: 18px; font-style: normal; font-variant-caps: normal;
font-weight: normal; letter-spacing: normal; text-align: start;
text-indent: 0px; text-transform: none; white-space: normal; word-spacing:
0px; -webkit-text-stroke-width: 0px; float: none; display: inline
!important;">List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[9]
List rules font-size: 18px; font-style: normal; font-variant-caps:
normal; font-weight: normal; letter-spacing: normal; text-align: start;
text-indent: 0px; text-transform: none; white-space: normal; word-spacing:
0px; -webkit-text-stroke-width: 0px; float: none; display: inline
!important;">Check out or update participant
bios:
www.members.re-wrenches.org [11]
WWW.SWNL.NET [12]
Solarwinds Northernlights _ _ _ SERVING MID COAST MAINE ">
_ 207-832-7574
CL. 610-517-8401 _ _ __BLAIR "TUMP" MAY_
******** MAINE'S CHARTER
********
_ __ NABCEP "CERTIFIED PV INSTALLER"_
******** MAINE'S CHARTER
********
_ TRACE XANTREX "CERTIFIED" DEALER / INSTALLER"_
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3] mailto:glenn.burt at glbcc.com
[4]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[5]
mailto:petertor at pobox.com
[6] mailto:RE-wrenches at lists.re-wrenches.org
[7]
mailto:RE-wrenches at lists.re-wrenches.org
[8]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[9]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[10]
http://www.re-wrenches.org/etiquette.htm
[11]
http://www.members.re-wrenches.org/
[12]
http://webmail.sti.net/blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200812/a24f27eb/attachment.htm>
More information about the RE-Wrenches
mailing list