Seems like over kill and I too am wondering why use anything but UL listed wire. I always use tinned cable from Cobra. They have the “X FLEX” and the “X FLEX 150” the X flex #2AWG is good for 213 Amps 2/0 is good for 336 Amps. The X FLEX 150 #2AWG is good for 255 and the 2/0 is good for 390 Amps. Let me know off list if you wold like my sales rep, Good quick service. T
> On Aug 11, 2020, at 10:34 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:
>
> Okay I have to ask, why wouldn’t you want to stick to code compliant battery cabling?
>
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of petertor at pobox.com <mailto:petertor at pobox.com>
> Sent: Tuesday, August 11, 2020 6:18 PM
> To: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Ampacity Ratings for Different Conductors
>
> I have been designing a off-grid system that can fit in an outside-accessible compartment with an approximate 24" square footprint and space above about 18" - 24".
>
> I am using two Battle Born LiFePO4 batteries rated at 24 V / 50 Ah, a Cotek pure sine wave inverter with an output power of 4,000 VA , a MorningStar TS-MPPT-60 charge controller, a Victron BMV-712 "coulomb counter" and a Battle Born surge limiter CL500.
>
> The current limiter limits the current to 120 continuous, and 200 A for 30 sec.
>
> I have been able to fit everything in and I am designing the cabling, and here is my problem.
>
> I have one vendor that recommends Ancor brand Tinned Marine Grade Battery Cable. It is "resistant to salt water, battery acid, oil, gasoline, heat, abrasion and ultra-violet radiation. Exceeds UL 1426, ABYC and US Coast Guard Charter boat (CFR Title 46) standards. Highest quality ultra-flexible (Type 3) tinned copper stranding. Vinyl insulation. -50 deg-C to 105 deg-C." 2 AWG is composed of 665 ea 30 AWG stands.
>
> The same vendor has "welding cable" with an EPDM insulation rated at 600 V, water/chemical/grease/abrasion resistant, -50 deg-C to 105 deg-C, "marine grade". Not UL listed. 624 ea 30 AWG strands.
>
> Roughly comparable pricing.
>
> They claim both 2 AWG cables are rated at 210 A. Not sure if this is continuous duty or whether I should derate this for what will be continuous duty.
>
> This is new territory for me, and any help would be appreciated.
>
> Peter T. Parrish, Ph.D.
> President, California Solar Engineering
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net> www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>