[RE-wrenches] protecting wire below 8' w/awning array
Ray
ray at solarray.com
Sat Jul 18 18:56:49 EDT 2020
I've always interpreted this rule to mean to the wiring, not to the
bottom edge of the array. 110.27 refers to live parts; that's actual
uninsulated bare conductors, lugs, or switch contacts, etc. Further,
690.31(A) just says "circuit conductors shall be guarded...." Finally,
if the conductors are within 8 ft of the ground, then usually you can
just put a plastic shield, or expanded aluminum lathe on the bottom of
the rails to protect the conductors.
Wire Shielding ground Mount
I pinched this pic from Miller Solar, one of our long time wrenches here.
Ray Walters
Remote Solar
303 505-8760
On 7/18/20 3:57 PM, Dave Angelini Offgrid Solar wrote:
>
> I would give a small amount of additional time to convince the
> inspector. After that I would build the fence he wants. I would also
> build it to be easily dismantled/removed. Good Luck!
>
>
> *Dave Angelini Offgrid Solar "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net
> <mailto:offgridsolar at sti.net> text 209 813 0060*
>
> On Sat, 18 Jul 2020 10:05:49 -0400, Kirk Herander <vtsolar at icloud.com>
> wrote:
>
>> Thanks all. The NEC reference 110.27 is helpful.
>> I am in a battle now with my AHJ building inspector which relates
>> indirectly to the 8' rule question. I have mounted several modules
>> awning-style above a window at an angle of 30 degrees. The bottom of
>> the array is 7' from grade. The inspector insists that this is a
>> ground-mount array, even though it is mounted on the wall of a
>> habitable building. He cites NFPA 1, 2012 fire safety rules which are
>> adopted in my locale. In his brain, I must add a fence to insure no
>> one can touch the array within 10' per NFPA access guidelines for
>> ground-mounts.
>> The NFPA does not cover wall-mounts specifically, if at all. It only
>> defines arrays on buildings (roof) and "real" ground mounts, i.e.
>> mounted on a detached structure.
>> The exposed PV wire enters a J-box roughly 10' above grade(behind the
>> array), more than complying with guidance in NEC 110.27. I am using
>> this rule as backup to my position that NFPA fire safety rules for
>> ground mounts do not apply, and the wire runs are protected
>> accordingly per the NEC. IMO the intent of the NFPA 10' ground-mount
>> rule is to protect the array and specifically wiring from damage,
>> which compliance with NEC 110.27 already does.
>>
>> On 7/18/2020 4:01:34 AM, Martin Herzfeld <findsolar at herzfeld.org>
>> wrote:
>>
>> Simply, the '2.5 m' (8 ft) has been inferred from Article
>> 110.27(A)(4). It's interesting now that the distance in the 2019
>> CEC/2017 NEC has increased based on voltage. In other words, if
>> the voltage is greater than 301 volts the minimum would be 8 ft 6
>> in. :)
>>
>> All the best,
>>
>> Martin Herzfeld, Interstate Renewable Energy Council (IREC)
>> Certified Master Trainer ™ for Photovoltaics (PV) Installation
>> Professional #IREC 10037
>> Contract Training Provider (CTP)
>> Adjunct Professor, Energy
>>
>> California Solar & Electrical Contractor License #00833782 C46,
>> C10, D56, D31, C-7
>> Solar, Electrical, Trenching, Pole Installation & Maintenance,
>> Instrumentation
>>
>> Contract Solar (PV) Technical Inspector - 3rd Party Inspections
>> Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
>> OSHA-Authorized Construction Trainer #32-0105338
>> CompTIA Certified Technical Classroom Trainer (CTT+)
>> #T3NSZCNBBKB4QTQG
>>
>> * Professional Member, International Association of Electrical
>> Inspectors #7035507 - Since 2006
>> * Accredited and Registered North American Board of Certified
>> Energy Practitioners (NABCEP) Continuing Education (CE) Training
>> Provider
>>
>> On Fri, Jul 17, 2020, 7:32 PM August Goers <august at luminalt.com
>> <mailto:august at luminalt.com>> wrote:
>>
>> Hi Kirk - We work in San Francisco where they have a local
>> code amendment:
>> <https://codelibrary.amlegal.com/codes/san_francisco/latest/sf_building/0-0-0-84935>
>>
>> 300.4(I) Add the following section:
>> (I) Subject to Physical Damage. Premises wiring systems
>> installed less than 2.44 m (8 feet) above a walking surface
>> or finished floor are considered subject to physical damage.
>> As far as I'm aware otherwise, there is not a specific
>> definition specifying 8' for physical damage in the broader
>> NEC - I think it's just up to the AHJ.
>> August
>> Luminalt
>>
>>
>> On Fri, Jul 17, 2020 at 8:38 AM Kirk Herander
>> <vtsolar at icloud.com <mailto:vtsolar at icloud.com>> wrote:
>>
>> All,
>> Is there a reference to this so-called "8-foot rule" that
>> someone could point me to in the NEC? Thanks.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <http://www.members.re-wrenches.org>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>> _______________________________________________ List sponsored by
>> Redwood Alliance List Address: RE-wrenches at lists.re-wrenches.org
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check
>> out or update participant bios: www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200718/5e994737/attachment.htm>
More information about the RE-Wrenches
mailing list