[RE-wrenches] White wire for DC- after ground fault breaker

Mac Lewis maclewis1 at gmail.com
Sun Jun 14 08:08:27 EDT 2020


James,

I might open the ground fault breaker and show him with the ohmmeter that
this is not a solidly grounded system.  You are absolutely correct with
this and if he gets tough just let him know you need him to sign off
personally that you had informed him of this exact code reference.  Or he
may sign off from the office...

On Sat, Jun 13, 2020 at 7:21 PM Kent Osterberg <kent at coveoregon.com> wrote:

> James,
>
> Here's the code reference: 2017 690.31(B)(1). Only solidly grounded PV
> system conductors shall be marked in accordance with 200.6 (white or gray).
>
> Kent Osterberg
> Blue Mountain Solar
>
>
> On 6/13/2020 5:56 PM, James Jarvis wrote:
>
> Brian, thank you very much. With your hint of "functional ground" I can
> clearly see that I am not allowed to have those be white wires.
>
> Now time for me to incur the full wrath by daring to question the infinite
> wisdom of the "highly qualified individual" from the state.
>
> (all kinds of fun stuff from this guy. Got another violation for having a
> donut type current transformer over a line voltage wire. He said that
> wasn't allowed.)
>
> Thank you,
>
> -James Jefferson Jarvis
> APRS World, LLC
> +1-507-454-2727
>
> (Sent from my phone. My apologies for spelling errors and brevity.)
>
> On Sat, Jun 13, 2020, 17:41 Brian Mehalic <brian at solarenergy.org> wrote:
>
>> Change in 2017 to “functional grounded” was to clarify this - it’s not
>> solid when it is thru a fuse or breaker than can be interrupted either in
>> the event of a ground-fault or if the breaker is intentionally opened. 2017
>> makes it clear that there are very few solidly grounded systems (2 or less
>> PV source circuits, not touching a building the only case it is allowed).
>> Pardon any incorrect language as I don’t have my code book, but I do think
>> the 2017 NEC® makes it very clear, including in the definition of function
>> grounded, that those conductors cannot be white or gray, regardless of if
>> the system has a transformer-based or TL inverter or a CC with integrated
>> or an external GF breaker/fuse.
>>
>> Brian
>>
>> > On Jun 13, 2020, at 3:05 PM, greg egan <greg at remotepowerinc.com> wrote:
>> >
>> > Jim,  Hope all is well with you and yours.  on white wires in
>> circuits, In 3 ph. circuits you can get killed breaking into a neutral
>> that's common to other circuits.  One example, working on 277 lighting, you
>> throw the breaker or light switch on the one circuit you're working so the
>> hot isn't hot anymore.  It's standard practice for 3 ph. lighting ckts to
>> share a neutral.  The white wire in your ckt is wire nutted in the j-box up
>> in the ceiling to the common neutrals.  Those neutrals are hot to ground
>> when their respective ckts are hot and they're carrying current.
>> >
>> > Just thought it was worth mentioning on this list that there's no hard
>> fast rule that all white wires are dead.  It depends on the ckt.
>> >
>> > Best,
>> > Greg Egan
>> > Remote Power Inc.
>> >
>> >
>> > Message: 11
>> > Date: Fri, 12 Jun 2020 15:17:19 -0500
>> > From: James Jarvis<jj at aprsworld.com>
>> > To: RE-wrenches<re-wrenches at lists.re-wrenches.org>
>> > Subject: [RE-wrenches] White wire for DC- after ground fault breaker
>> > Message-ID:
>> >    <CAFWEuYVMACXebixHtyRVYQ5Xnmaur=UgTv6Etu5TNEpm00nhoA at mail.gmail.com>
>> > Content-Type: text/plain; charset="utf-8"
>> >
>> > Hello Wrenches,
>> >
>> > I have an off-grid install where I was recently red-tagged by the state
>> > inspector. System is 24 volt with battery, Magnum inverters, some Magnum
>> > charge controllers, and a Morningstar charge controller. It is permitted
>> > under NEC 2017.
>> >
>> > One of the inspectors issues was that my DC- conductors to the array /
>> > rapid shut down box are black color. He wants them to be white because
>> he
>> > says they are solidly grounded. I reason that they are only solidly
>> > grounded when they are solidly grounded. As soon as the ground fault
>> > protection breaker opens, they are floating at array voltage. I think
>> it is
>> > misleading and unsafe to have a white conductor that can have hundreds
>> of
>> > volts of potential on it when a breaker trips.
>> >
>> > I haven't dug into the code yet. I'm just working on the logic that one
>> of
>> > my mentors put into me which is white wires better not have voltage
>> > potential on them. "That's the sort of sh*t that kills electricians" is
>> > what he repeatedly said ... and it's stuck with me.
>> >
>> > Thoughts? I'm backed into the corner with the state, so I will be
>> changing
>> > them to white even if it is unsafe ... unless I have some code backing.
>> >
>> > <rant>Changing the wires to white will get interesting up on the roof. I
>> > wonder if they want me to cut off the black MC on the modules and
>> replace
>> > them with white? This is mostly just an exercise in the State of
>> Minnesota
>> > only wanting to know about and allow micro inverters. They brought in a
>> > state inspector from three hours away who kept repeating that he was a
>> > "highly qualified individual", but was unable to identify or recognize a
>> > charge controller. He kept referring to the charge controllers as
>> > inverters.</rant off>
>> >
>> > Thanks,
>> >
>> > -James Jarvis
>> > APRS World, LLC
>> > +1-507-454-2727
>> > http://www.aprsworld.com/
>> > -------------- next part --------------
>> > An HTML attachment was scrubbed...
>> > URL:<
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200612/5cd338c8/attachment-0001.html
>> >
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200614/a776d91a/attachment.htm>


More information about the RE-Wrenches mailing list