[RE-wrenches] White wire for DC- after ground fault breaker

Kent Osterberg kent at coveoregon.com
Sat Jun 13 21:21:55 EDT 2020


James,

Here's the code reference: 2017 690.31(B)(1). Only solidly grounded PV 
system conductors shall be marked in accordance with 200.6 (white or gray).

Kent Osterberg
Blue Mountain Solar


On 6/13/2020 5:56 PM, James Jarvis wrote:
> Brian, thank you very much. With your hint of "functional ground" I 
> can clearly see that I am not allowed to have those be white wires.
>
> Now time for me to incur the full wrath by daring to question the 
> infinite wisdom of the "highly qualified individual" from the state.
>
> (all kinds of fun stuff from this guy. Got another violation for 
> having a donut type current transformer over a line voltage wire. He 
> said that wasn't allowed.)
>
> Thank you,
>
> -James Jefferson Jarvis
> APRS World, LLC
> +1-507-454-2727
>
> (Sent from my phone. My apologies for spelling errors and brevity.)
>
> On Sat, Jun 13, 2020, 17:41 Brian Mehalic <brian at solarenergy.org 
> <mailto:brian at solarenergy.org>> wrote:
>
>     Change in 2017 to “functional grounded” was to clarify this - it’s
>     not solid when it is thru a fuse or breaker than can be
>     interrupted either in the event of a ground-fault or if the
>     breaker is intentionally opened. 2017 makes it clear that there
>     are very few solidly grounded systems (2 or less PV source
>     circuits, not touching a building the only case it is allowed).
>     Pardon any incorrect language as I don’t have my code book, but I
>     do think the 2017 NEC® makes it very clear, including in the
>     definition of function grounded, that those conductors cannot be
>     white or gray, regardless of if the system has a transformer-based
>     or TL inverter or a CC with integrated or an external GF
>     breaker/fuse.
>
>     Brian
>
>     > On Jun 13, 2020, at 3:05 PM, greg egan <greg at remotepowerinc.com
>     <mailto:greg at remotepowerinc.com>> wrote:
>     >
>     > Jim,  Hope all is well with you and yours.  on white wires in
>     circuits, In 3 ph. circuits you can get killed breaking into a
>     neutral that's common to other circuits.  One example, working on
>     277 lighting, you throw the breaker or light switch on the one
>     circuit you're working so the hot isn't hot anymore.  It's
>     standard practice for 3 ph. lighting ckts to share a neutral.  The
>     white wire in your ckt is wire nutted in the j-box up in the
>     ceiling to the common neutrals. Those neutrals are hot to ground
>     when their respective ckts are hot and they're carrying current.
>     >
>     > Just thought it was worth mentioning on this list that there's
>     no hard fast rule that all white wires are dead.  It depends on
>     the ckt.
>     >
>     > Best,
>     > Greg Egan
>     > Remote Power Inc.
>     >
>     >
>     > Message: 11
>     > Date: Fri, 12 Jun 2020 15:17:19 -0500
>     > From: James Jarvis<jj at aprsworld.com <mailto:jj at aprsworld.com>>
>     > To: RE-wrenches<re-wrenches at lists.re-wrenches.org
>     <mailto:re-wrenches at lists.re-wrenches.org>>
>     > Subject: [RE-wrenches] White wire for DC- after ground fault breaker
>     > Message-ID:
>     >   
>     <CAFWEuYVMACXebixHtyRVYQ5Xnmaur=UgTv6Etu5TNEpm00nhoA at mail.gmail.com
>     <mailto:UgTv6Etu5TNEpm00nhoA at mail.gmail.com>>
>     > Content-Type: text/plain; charset="utf-8"
>     >
>     > Hello Wrenches,
>     >
>     > I have an off-grid install where I was recently red-tagged by
>     the state
>     > inspector. System is 24 volt with battery, Magnum inverters,
>     some Magnum
>     > charge controllers, and a Morningstar charge controller. It is
>     permitted
>     > under NEC 2017.
>     >
>     > One of the inspectors issues was that my DC- conductors to the
>     array /
>     > rapid shut down box are black color. He wants them to be white
>     because he
>     > says they are solidly grounded. I reason that they are only solidly
>     > grounded when they are solidly grounded. As soon as the ground fault
>     > protection breaker opens, they are floating at array voltage. I
>     think it is
>     > misleading and unsafe to have a white conductor that can have
>     hundreds of
>     > volts of potential on it when a breaker trips.
>     >
>     > I haven't dug into the code yet. I'm just working on the logic
>     that one of
>     > my mentors put into me which is white wires better not have voltage
>     > potential on them. "That's the sort of sh*t that kills
>     electricians" is
>     > what he repeatedly said ... and it's stuck with me.
>     >
>     > Thoughts? I'm backed into the corner with the state, so I will
>     be changing
>     > them to white even if it is unsafe ... unless I have some code
>     backing.
>     >
>     > <rant>Changing the wires to white will get interesting up on the
>     roof. I
>     > wonder if they want me to cut off the black MC on the modules
>     and replace
>     > them with white? This is mostly just an exercise in the State of
>     Minnesota
>     > only wanting to know about and allow micro inverters. They
>     brought in a
>     > state inspector from three hours away who kept repeating that he
>     was a
>     > "highly qualified individual", but was unable to identify or
>     recognize a
>     > charge controller. He kept referring to the charge controllers as
>     > inverters.</rant off>
>     >
>     > Thanks,
>     >
>     > -James Jarvis
>     > APRS World, LLC
>     > +1-507-454-2727
>     > http://www.aprsworld.com/
>     > -------------- next part --------------
>     > An HTML attachment was scrubbed...
>     >
>     URL:<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200612/5cd338c8/attachment-0001.html>
>     >
>     > _______________________________________________
>     > List sponsored by Redwood Alliance
>     >
>     > List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>     >
>     > Change listserver email address & settings:
>     > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     >
>     > List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>     >
>     > List rules & etiquette:
>     > www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>     >
>     > Check out or update participant bios:
>     > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>     >
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200613/727a989c/attachment.htm>


More information about the RE-Wrenches mailing list