[RE-wrenches] magnum question
Lones Tuss
ltuss at outbackpower.com
Thu Apr 2 11:46:24 EDT 2020
Hi Jay
The FXR inverters do have the ability to run 2 legs of a 3phase system on a single Mate3(s)and a Hub10.3
Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be arranged so the inverters are set to a 3 phase
configuration.
Up to 9 inverters can be used per system, up to 3 inverters per ac phase.
Up to 6 inverters can be used with up to 3 inverters per phase on 2 of the ac legs a 3phase system.
For more information on the jumper locations see the Hub 10.3 quick start guide.
http://www.outbackpower.com/downloads/documents/system_management/hub/hub103_quick_start.pdf
In a 3 phase system the inverters are programmed as Master, B phase Master, C Phase Master or designated as a Slave inverter.
Each Master can control 2 slave inverters.
This is further explained in the FXR installation manual.
http://www.outbackpower.com/downloads/documents/inverter_chargers/fxr_vfxr_a/fxr_install.pdf
I hope this helps.
Take Care All
-----Original Message-----
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of jay
Sent: Wednesday, April 1, 2020 4:39 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] magnum question
Hi All,
My question is can a single Magnum remote run 2 inverters each as master for 120v?
I’ve got a client with a 3 phase generator, and I need two phases, but I don’t need 240v.
1. I can’t change the generator
2. Two phases because I can’t load one phase that heavily.
I can do 2 Outback FXR’s each as a master, but I’d need to have 2 Mate3S’s.
But I don’t know if magnum has that possiblity?
Thanks
jay
Peltz Power
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
https://protect2.fireeye.com/v1/url?k=d4abb431-890cfaf3-d4a8bdba-002590870bde-fe8439a98f146def&q=1&e=cc596888-1eac-4ff2-b73a-fe4a7f887cd6&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
https://protect2.fireeye.com/v1/url?k=6fb987e8-321ec92a-6fba8e63-002590870bde-aa16baf4f942a9e8&q=1&e=cc596888-1eac-4ff2-b73a-fe4a7f887cd6&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm
Check out or update participant bios:
https://protect2.fireeye.com/v1/url?k=744e5f95-29e91157-744d561e-002590870bde-8fb79a89726d0b65&q=1&e=cc596888-1eac-4ff2-b73a-fe4a7f887cd6&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F
More information about the RE-Wrenches
mailing list