Jay:
This idea sounds wrong on many levels. Generators are designed to be
loaded evenly, with some allowance for normal deviations. Having separate
loads that can vary independently is asking for regulation problems.
You did not state if the generator was wound Wye or Delta. This makes a
difference.
Delta wound generators that provide 120/240 have one winding
center-tapped. That winding can provide only 1/3 of the rating of the
generator (there is some research that says the de-rate is greater). If
this is the case, your two inverters can each access only 1/6 of the
generator capability. Sure you might be able to draw more than 1/6, for a
while...
Have you checked to see if the generator can be field re-tapped to provide
120 only? Then you could provide a generator-fed distribution and put all
of your 120 loads on it, providing the full generator capability.
It has come to my attention recently that two Outback FXR (or FX, I am not
sure) inverters can be stacked on two legs of a three-phase input power
source. I had thought this was not possible. I know it works because I
accidently did this. I believe the supply was Wye configured. It was with
a mobile set up built by someone else. The inverters should have been the
Mobile version, and maybe this is what made this possible. You just can't
use an X240 on this setup. Consider this option if you must unbalance the
generator. Try to balance the loads and charging between the inverters and
avoid power-save settings (you can't power-save without an X240 anyway).
I have had many customers ask me to do something that my intuition told me
was a bad idea. When I was younger I might comply, and learn to regret
it. Good luck and stay strong.
William Miller
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of jay
Sent: Wednesday, April 1, 2020 4:39 PM
To: RE-wrenches
Subject: [RE-wrenches] magnum question
Hi All,
My question is can a single Magnum remote run 2 inverters each as master
for 120v?
I’ve got a client with a 3 phase generator, and I need two phases, but I
don’t need 240v.
1. I can’t change the generator
2. Two phases because I can’t load one phase that heavily.
I can do 2 Outback FXR’s each as a master, but I’d need to have 2
Mate3S’s.
But I don’t know if magnum has that possiblity?
Thanks
jay
Peltz Power
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200402/235facae/attachment.htm>
More information about the RE-Wrenches
mailing list